Baxi solo 50 /4 RS. Boiler would go out after a few minutes or a few seconds with a click. Got it to stay on for a couple of hours once but not again.
Called in the gas man who said it was ancient and we needed a new one which they could fit next Tuesday. Otherwise it would need a new gas valve. They could fit a new boiler inside 4 days but couldn't get the part for 10 days (!). So I got one for them in 48 hours. They fitted it and said it probably also needed the overheat thermostat. At least they only charged us cost for that.
Now 2 weeks later same problem happens again. After finding the baxi manual here https://www.dhsspares.co.uk/userfiles/Boiler_Manuals/BAX262.pdf I investigate further. Staring at the pilot light I can see it flickering, it is a windy day. Lighting the boiler I see the pilot light very unstable after the burner goes on full. Pilot light disappears - click - boiler goes out.
Moving the thermocouple connection I find the nut wiggles freely. If the Gas Safe man leaves it like that it can't need a gas tight connection (?!?). To cut a long story short I cleaned the pilot light injector and it now has a much stronger flame and the boiler is working again. So probably did not need the £250 work that was carried out.
Yes I will get it serviced/checked as quickly as possible (It is New Years Day). However my experience suggests that just being Gas Safe registered does not make an engineer competent or trustworthy.
Called in the gas man who said it was ancient and we needed a new one which they could fit next Tuesday. Otherwise it would need a new gas valve. They could fit a new boiler inside 4 days but couldn't get the part for 10 days (!). So I got one for them in 48 hours. They fitted it and said it probably also needed the overheat thermostat. At least they only charged us cost for that.
Now 2 weeks later same problem happens again. After finding the baxi manual here https://www.dhsspares.co.uk/userfiles/Boiler_Manuals/BAX262.pdf I investigate further. Staring at the pilot light I can see it flickering, it is a windy day. Lighting the boiler I see the pilot light very unstable after the burner goes on full. Pilot light disappears - click - boiler goes out.
Moving the thermocouple connection I find the nut wiggles freely. If the Gas Safe man leaves it like that it can't need a gas tight connection (?!?). To cut a long story short I cleaned the pilot light injector and it now has a much stronger flame and the boiler is working again. So probably did not need the £250 work that was carried out.
Yes I will get it serviced/checked as quickly as possible (It is New Years Day). However my experience suggests that just being Gas Safe registered does not make an engineer competent or trustworthy.