Hi all,
I have a Baxi Solo PFL System 60 and I think I may have a problem with the Expansion Vessel. Reasons:
The system has several rads, one of which does not have a TRV and is permanently open, therefore there is always flow round the system. I also have a 'cool down' loop built in.
There is no air in the system.
I can find no leaks in the system.
With the start pressure set to 1 bar, on firing up, over 10 - 15 mins the system runs up to over 3 bar, ie into the red zone. The pressure relief valve then opens sending v hot water down the overflow pipe. It shuts off at around 3 bars and the system runs normally.
When the system cools down (ie overnight) the pressure runs down well below 1 bar - in fact the pressure gauge needle is on the low stop - ie 0 bar. I then re-pressurise to the specified 1 bar and the whole thing happens again.
As the experts will know, the boiler has a red expansion vessel built in at the back rhs. The manual says this should be pressurised to 1 bar. There is what I think is a pressure test tube below the expansion vessel running from Lt to Rt and ending in a car type valve. When I tried to connect a pressure tester to this water came out under pressure.
Questions:
1, obviously, do you think my analysis is correct?
2. Should there be water or air in the expansion vessel (if it should be water, I don't see how it can do anything).
3. If air, is it faulty, and if so what do I do, and
4 If it's not faulty how do I drain it and how do I re-pressurise?
4. If all the above is wrong, how should I proceed?
Thanks,
Swin.
I have a Baxi Solo PFL System 60 and I think I may have a problem with the Expansion Vessel. Reasons:
The system has several rads, one of which does not have a TRV and is permanently open, therefore there is always flow round the system. I also have a 'cool down' loop built in.
There is no air in the system.
I can find no leaks in the system.
With the start pressure set to 1 bar, on firing up, over 10 - 15 mins the system runs up to over 3 bar, ie into the red zone. The pressure relief valve then opens sending v hot water down the overflow pipe. It shuts off at around 3 bars and the system runs normally.
When the system cools down (ie overnight) the pressure runs down well below 1 bar - in fact the pressure gauge needle is on the low stop - ie 0 bar. I then re-pressurise to the specified 1 bar and the whole thing happens again.
As the experts will know, the boiler has a red expansion vessel built in at the back rhs. The manual says this should be pressurised to 1 bar. There is what I think is a pressure test tube below the expansion vessel running from Lt to Rt and ending in a car type valve. When I tried to connect a pressure tester to this water came out under pressure.
Questions:
1, obviously, do you think my analysis is correct?
2. Should there be water or air in the expansion vessel (if it should be water, I don't see how it can do anything).
3. If air, is it faulty, and if so what do I do, and
4 If it's not faulty how do I drain it and how do I re-pressurise?
4. If all the above is wrong, how should I proceed?