Hi! We are having a problem with our(the landlords) boiler or the programmer. The boiler is a Baxi solo3 and the programmer a honeywell 6400. We have not had any hot water since yesterday, I just can't get it to work. When I put the HW on the CH comes on instead. Is this going to be difficult and costly to fix, because we don't have our landlords phone number :confused: And so we'll have to pay for it ourselves if we want to have a wash before next week.
 
Sponsored Links
Most likely the problem is with the motorised valve(s) on your system. If the boiler can do heating OK - there's nothing wrong with it.

Have a look in the cupboard where the hot water cylinder is, for a silver-coloured box with two or three pipes connected to it. That's a motorised valve. Chances are the motor's failed (if no changes have been made to the system and it worked OK before). The motor costs £12 - £15 and takes about half an hour to fit.

BUT it takes a competent heating engineer to work out whether the problem is the motor or something else.
 