I'm trying to learn a few things while attempting to do some basic diagnosis of what may have caused a problem with my central heating.
I have a Glowworm flexicom 15hx gas boiler for hot water and central heating, with a Drayton LP241 programmer/controller.
These heat my hot water just fine. However, recently, my central heating has stopped working; when the controller enables central heating, the boiler does not fire up.
I also notice that, with the controller's central heating on/enabled, the room thermostat (Drayton RTS1 230V mains) has no click in any position.
I understand that this thermostat needs 230V mains AC power and so have measured the voltage across the live and neutral terminals on the thermostat's wall mount. When the controller sets the central heating on and lights up the central heating indicator, my multimeter's AC voltage reading shows 241V across the live and neutral terminals. When the controller sets central heating off, I read 13V across the same live-neutral terminals (is this to be expected or the sign of a problem?).
The controller/programmer's data sheet (https://www.draytoncontrols.co.uk/sites/default/files/2812_D41-11_LP & LPSi Data Sheet.pdf) has the following wiring schematics, which I'll admit to knowing very little about -
Initially, I also just checked some basic things like my house main fuse box, which has no fuses tripped.
There's a wall switch with the 3A fuse, next to the heating and hot water controller. Turning this off turns off all power to both the controller and the gas boiler (at least the boiler's LCD display goes off).
I don't think there's a problem with that switch's 3A fuse; It's still working, otherwise the controller and boiler's display would be off, right?
The boiler doesn't show any error codes either.
The central heating pressure is reading the same as always (around 1.2 bar).
A replacement room thermostat is £16, so I went and bought a new one (same model) and put it on the same wall mount plate. Then, with the programmer/controller enabling central heating, I noticed that this thermostat now did have a demand click, only the boiler still wouldn't fire up, yet it still fires up when the controller enables hot water.
However, a day later, still with the new thermostat fitted, I again turn the central heating on and go to waggle the thermostat dial and notice it now has no click in any position, which is a bit puzzling. I take it off and still measure 241V across live-neutral (when the controller sets C.H. on; 13V when off). Should I be able to test if the new thermostat has inexplicably broken within a day or is still working by (carefully) connecting it to a normal mains power socket and checking that it clicks?
I did find some diagnostic pages in my boiler's installation manual -
This would lead me to 'Consult the state list' (although I'm now not sure if the new thermostat is correctly signalling), but when accessing the state list, my boiler flashes 'S 30', which isn't mentioned anywhere, as far as I can see. What does S 30 mean?
I've now run out of my very limited knolwedge and ideas.
I'm wondering if there could be a problem with the thermostat's connections to the terminals on the back plate: Can I bypass a problematic thermostat or wiring and simply wire the thermostat's 'live' to 'call/3' terminals to just always signal demand?
Then, even with the thermostat circuit always signalling demand, if the central heating still doesn't fire up, where would that leave a problem?
Could I, for example, hard wire the room thermostat demand signal right on the programmer/controller's back-plate terminals, eliminating/reducing a wiring problem somewhere on the way to the room thermostat circuit?
Or perhaps I've misunderstood things and maybe the thermostat demand signal is combined with the controller's central heating on/enabled signal within the flexicom boiler's electronics itself.
Although it's something I think is almost certainly not somewhere I'm prepared to go, I was still wondering if it's even technically possible to entirely eliminate both the controller and thermostat from consideration by (temporarily) connecting some central heating demand terminals in the boiler's electronics box.
Also, at this point, given that the boiler fires up for hot water OK, who, out of an electrician or gas boiler engineer, would tend to be best suited to further investigate and fix this issue?
Finally, is there anything else you can suggest I look at or try?
I have a Glowworm flexicom 15hx gas boiler for hot water and central heating, with a Drayton LP241 programmer/controller.
These heat my hot water just fine. However, recently, my central heating has stopped working; when the controller enables central heating, the boiler does not fire up.
I also notice that, with the controller's central heating on/enabled, the room thermostat (Drayton RTS1 230V mains) has no click in any position.
I understand that this thermostat needs 230V mains AC power and so have measured the voltage across the live and neutral terminals on the thermostat's wall mount. When the controller sets the central heating on and lights up the central heating indicator, my multimeter's AC voltage reading shows 241V across the live and neutral terminals. When the controller sets central heating off, I read 13V across the same live-neutral terminals (is this to be expected or the sign of a problem?).
The controller/programmer's data sheet (https://www.draytoncontrols.co.uk/sites/default/files/2812_D41-11_LP & LPSi Data Sheet.pdf) has the following wiring schematics, which I'll admit to knowing very little about -
Initially, I also just checked some basic things like my house main fuse box, which has no fuses tripped.
There's a wall switch with the 3A fuse, next to the heating and hot water controller. Turning this off turns off all power to both the controller and the gas boiler (at least the boiler's LCD display goes off).
I don't think there's a problem with that switch's 3A fuse; It's still working, otherwise the controller and boiler's display would be off, right?
The boiler doesn't show any error codes either.
The central heating pressure is reading the same as always (around 1.2 bar).
A replacement room thermostat is £16, so I went and bought a new one (same model) and put it on the same wall mount plate. Then, with the programmer/controller enabling central heating, I noticed that this thermostat now did have a demand click, only the boiler still wouldn't fire up, yet it still fires up when the controller enables hot water.
However, a day later, still with the new thermostat fitted, I again turn the central heating on and go to waggle the thermostat dial and notice it now has no click in any position, which is a bit puzzling. I take it off and still measure 241V across live-neutral (when the controller sets C.H. on; 13V when off). Should I be able to test if the new thermostat has inexplicably broken within a day or is still working by (carefully) connecting it to a normal mains power socket and checking that it clicks?
I did find some diagnostic pages in my boiler's installation manual -
This would lead me to 'Consult the state list' (although I'm now not sure if the new thermostat is correctly signalling), but when accessing the state list, my boiler flashes 'S 30', which isn't mentioned anywhere, as far as I can see. What does S 30 mean?
I've now run out of my very limited knolwedge and ideas.
I'm wondering if there could be a problem with the thermostat's connections to the terminals on the back plate: Can I bypass a problematic thermostat or wiring and simply wire the thermostat's 'live' to 'call/3' terminals to just always signal demand?
Then, even with the thermostat circuit always signalling demand, if the central heating still doesn't fire up, where would that leave a problem?
Could I, for example, hard wire the room thermostat demand signal right on the programmer/controller's back-plate terminals, eliminating/reducing a wiring problem somewhere on the way to the room thermostat circuit?
Or perhaps I've misunderstood things and maybe the thermostat demand signal is combined with the controller's central heating on/enabled signal within the flexicom boiler's electronics itself.
Although it's something I think is almost certainly not somewhere I'm prepared to go, I was still wondering if it's even technically possible to entirely eliminate both the controller and thermostat from consideration by (temporarily) connecting some central heating demand terminals in the boiler's electronics box.
Also, at this point, given that the boiler fires up for hot water OK, who, out of an electrician or gas boiler engineer, would tend to be best suited to further investigate and fix this issue?
Finally, is there anything else you can suggest I look at or try?