Hi all,Im new to the forums and am after a spot of help or info.
My girlfreinds boiler a Biasi 24s!!!! has actually been fine since she had it installed in 2002,with just the odd spot of maintenance every now and again.
Just before xmas I noticed water dripping from the Prv outlet outside and she told me that she had to refill the system everytime she put the heating on.
So I spoke to my friend who works as a plumber and central heating installer for the local council and he said looks like the prv is faulty and to take it off and give it a check over.
I removed the Prv and yes it was black and gunged up inside,I tried to clean it out as a temp measure but it didnt work.
Ive now fitted a new Prv to the boiler and all is well,no dripping outside and it also holds its pressure too.
Today after fitting the valve i had the heating switched onto constant just to test it out but after about 10 minutes the boiler cut out.The trip switch stays in and the lock out lamp stays off.if i leave the boiler for say 2 minutes it will come back on,but then after afew mins of running it will cut out again!!! DHW is fine though,the boiler ingnites and hot water will flow from the tap.
It is just the central heatin that seems to be the problem.All the radiators have been bled and the pressure is at 1.3 bar. This is only happening since i replaced the PRV, and ive now drawn a blank!!!.One thing is for sure though,if i can get it sorted by the time the Gf comes home then she may not hit the roof!!!!!
can anyone help please
Lee
My girlfreinds boiler a Biasi 24s!!!! has actually been fine since she had it installed in 2002,with just the odd spot of maintenance every now and again.
Just before xmas I noticed water dripping from the Prv outlet outside and she told me that she had to refill the system everytime she put the heating on.
So I spoke to my friend who works as a plumber and central heating installer for the local council and he said looks like the prv is faulty and to take it off and give it a check over.
I removed the Prv and yes it was black and gunged up inside,I tried to clean it out as a temp measure but it didnt work.
Ive now fitted a new Prv to the boiler and all is well,no dripping outside and it also holds its pressure too.
Today after fitting the valve i had the heating switched onto constant just to test it out but after about 10 minutes the boiler cut out.The trip switch stays in and the lock out lamp stays off.if i leave the boiler for say 2 minutes it will come back on,but then after afew mins of running it will cut out again!!! DHW is fine though,the boiler ingnites and hot water will flow from the tap.
It is just the central heatin that seems to be the problem.All the radiators have been bled and the pressure is at 1.3 bar. This is only happening since i replaced the PRV, and ive now drawn a blank!!!.One thing is for sure though,if i can get it sorted by the time the Gf comes home then she may not hit the roof!!!!!
can anyone help please
Lee