Hi good evening
Fan spinning,
Pump working,
safety thermostat resistance ZERO,
Flue temp probe NTC, both CH and DHW temp Probes around 10K ohm,
Flow switch sensor Lamp on(RED) while DHW Tap running but off if central heating is swithed on,
Spark generator working as I can see bright spark,
checking Gas valve ----
check the On-Off operators coils
Pin 1 and Pin 3 no resistance i.e open circuit
Pin 1 and pin 4 no resistance i.e open circuit
(Approx 6400 ohm according to the service manual)
Pin 2 is an earth point
between Pin 3 and Pin 4 approx 900 ohm
does it mean the Gas valve is gone and need to be renewed.
please help