Big cooker
4 Feb 2007
Buckinghamshire
The wife has just ordered a new electric cooker on checking the spec it says its total load is 14.5 Kw . The length of cable run from consumer unit to cooker is 10m. The consumer unit is a split box with 100A main switch 2x32A 2x6A 1x20A 1x40A with 6mm cable to the old cooker. I propose to fit 16mm cable in conduit and a 50A mcb is this ok any comments would be helpful.
16mm will do fine for full load but the 50A MCB will not:
14500W/230V = 63.04A
Cooker diversity:
10A + 30% of remaining + 5A for socket
10A + 15.9A + 5A = 30.9A diversified load
So for your 10m run 6mm^2 on a 32A MCB will be sufficient.
You might want to check whether the cooker has terminals for 2 radials (oven + hob) as running a second 6mm^2 radial will be cheaper than ripping out the old and replacing with 16mm^2. (£2 vs. £5 per metre)
Davy
Try to persuade her to change it to one with gas burners on the hob. they're much better.
Thanks for the help. the fuse board is a new Volex and the biggest mcb that they make is a 50A or should i go for a different manufacturers mcb if any make more than 50A (also the cooker isolation switch from most manufactures is 45A ( i know it is not going to be switched on and off under load ) is this o.k any suggestions.
I wouldn't mix MCB's from different manufacturers if you can help it. As you said you won't get a cooker switch rated at more then 45A so you couldn't use it anyway.
You shouldn't fit an MCB with a rating higher than that of the lowest rated fitting/cable connected to it. As I said in my previous post, after diversity your current MCB and cable will be sufficient so you don't really need to upgrade anything.
I said:
You might want to check whether the cooker has terminals for 2 radials (oven + hob) as running a second 6mm^2 radial will be cheaper than ripping out the old and replacing with 16mm^2. (£20 vs. £50)
Davy
Most CU manfacturers do not sanction fitting more than one breaker of >40A.