Bit of plumbing advise PLEASE

Joined
12 Mar 2010
Messages
61
Reaction score
0
Location
Isle of Wight
Country
United Kingdom
Hi, Im looking at installing a couple of extra rads in my house (about 5000btu each) The central heating system is a drop system (upstairs ring main, then 3 drops to the downstairs rads) Question is, I was looking at tying into the upstairs ring and then doing a fourth drop for the two extra rads. Would it be best to use 22mm or 15mm pipe for the drop? Many thanks in advance
 
Sponsored Links
Hi, Im looking at installing a couple of extra rads in my house (about 5000btu each) The central heating system is a drop system (upstairs ring main, then 3 drops to the downstairs rads) Question is, I was looking at tying into the upstairs ring and then doing a fourth drop for the two extra rads. Would it be best to use 22mm or 15mm pipe for the drop? Many thanks in advance

15mm will be ok for the drops if taken from 22mm upstairs circuit
 
Sponsored Links
If its a straight drop ( not meters and meters away) you could even use microbore ;)
 