That's correct. However many boilers automatically restart at max output and then modulate down. Setting the max to, say, 15kW would reduce the "overload" on the rads and may extend the "on" periods.
I am surprised as the methodology, U-values etc, is based on work done by the Building Industry Research Association.
As the result is about twice what you anticipated, did you enter the height correctly? It asks for the height of a floor (which is multiplied by the number of floors), not the total height from ground floor to top ceiling.
You say that you have 8-9kW of rads. How did you arrive at this value?
Thanks for replies.
1. Yes, ok I did wonder how the modulation would work as it seems to be modulating down to around the min gas rate but I did gas rate when it was 60C plus flow temp so does the modulation control come in at higher flow temps. I suppose not range limiting helps with initial heat up.
2. Ok, yes I could try and do a bottom up calc from U values myself out of the SAP manual guidance on main construction elements. Takes a while though...and with a 1930s property, the estimates are pretty generic sometimes.
Ceiling height I put in 2.5M x 2 floors. Approx 10mx6m foot print. Semi. Cavity walls, no insulation in walls or suspended floor. I just did it again and this time 12.5kwh so a bit lower. It still feels a little high to me..
3. Rads outputs
Recently replaced Myson Premier - single panel
1. 1800 x 600 specs at delta 50C, 1.7kw
2. 1100 x 600 specs at delta 50C 1kw
Old (assumed) myson imperial single panel rads
3. 1290 x 600 - specs from myson single (1200x600) 1.1kw
4. 965 x 600 - specs from myson single (900x600) 0.8kw
5. 965 x 500 - specs from myson single (900x600) 0.8kw
6. Replaced Lounge single panel (unkown brand) 1800 x 600 use per myson premier 1.7kw
7. Towel rail 600 x 1000 guesstimate 0.4Kw
8. Conservatory double panel on frost setting, 1000x600 guesstuimate 1kw
Total excl conservatory 7.5kw
Total incl conservatory 8.5kw
On Sat it was -1C outside and took about 2 hours to climb 2.5C. Since it has warmed up a little since then the response is much faster, this morning I think the thermostat was off at 18.5C after about 1 hour in the morning...
So my logic is the heatloss can't be more than 7 or 8kw given that is the useable heat available inside from the rads.(plus internal gains but fairly insignificant?)...and it still heat.
Thanks again for your interest.