Boiler cutting out every 20 seconds for hot water

Joined
3 Dec 2007
Messages
239
Reaction score
1
Location
London
Country
United Kingdom
Hi all,

My combi boiler keeps cutting out every 20 to 30 seconds when the hot water is running and then refires and runs again for 20 seconds.the boiler is a Sabre HE (yes I know it's a crap unit). There are no fault lights showing!!
In the past the hot water and heating would cut out and the red fault light would come on but this was a simple fix cleaning out the pressure switch but this time it's different as the heating is working fine.

I'm a sparkie so electrics are no problem, but fault finding on boilers I could do with a little guidance.

I'm sure this is a simple fix of over heating and cutting out..


Thanks
 
Sponsored Links
Blocked plate heat exchanger on the primary side, nothing wrong with sabre boilers (rebadged vokera) .
 