I've been searching through the forum, but couldn't find any other examples of quite this problem... apologies if I missed one!
The basic problem is that the main flame in my boiler (a glow worm space saver mk2) tends to cut in and out when it should be on, for CH and/or HW.
Note that, unlike most threads I found on here, there is no problem with the pilot light, which remains lit through thick and thin. I've actually previously had a faulty thermocouple leading to the pilot light cutting out, and it ain't that this time!
I've checked the incoming voltage, and whenever the CH or HW should be calling for heat, I have 230v, so no problem with the timer, room thermostat etc.
I've also checked the voltage coming out of the boiler stat, and when the boiler isn't firing, it is zero. So, correct me if I'm wrong, but I think it can be narrowed down to one of three things:
1. Boiler stat is knackered
2. Thermocouple into boiler stat is knackered
3. Boiler is over-heating
I'm hoping I can rule out no3, as it would presumably come on again after a few minutes once cooled down, and it does not consistently do this - it will sometimes fail to fire after not having been on for several minutes. However, if there's anyway to confirm this, that would be great.
So that leaves 1 and 2. Now, sometimes when the boiler is failing to fire, if I turn up the level on the stat, it will kick in, but again, this isn't always the case. So not sure if that helps much!
I'm not actually clear on whether you can buy and fit the thermocouple separate to the whole stat - it certainly doesn't disconnect obviously, like the one for the pilot light on the gas valve does.
I guess if you can't separate them, then it's a moot point which is faulty, but if you can, the thermocouple will only be 1/10 of the price of the stat (which looks to be £50 or so).
So, any advice... does my understanding of what might be wrong make sense, and what options are there for fixing?
The basic problem is that the main flame in my boiler (a glow worm space saver mk2) tends to cut in and out when it should be on, for CH and/or HW.
Note that, unlike most threads I found on here, there is no problem with the pilot light, which remains lit through thick and thin. I've actually previously had a faulty thermocouple leading to the pilot light cutting out, and it ain't that this time!
I've checked the incoming voltage, and whenever the CH or HW should be calling for heat, I have 230v, so no problem with the timer, room thermostat etc.
I've also checked the voltage coming out of the boiler stat, and when the boiler isn't firing, it is zero. So, correct me if I'm wrong, but I think it can be narrowed down to one of three things:
1. Boiler stat is knackered
2. Thermocouple into boiler stat is knackered
3. Boiler is over-heating
I'm hoping I can rule out no3, as it would presumably come on again after a few minutes once cooled down, and it does not consistently do this - it will sometimes fail to fire after not having been on for several minutes. However, if there's anyway to confirm this, that would be great.
So that leaves 1 and 2. Now, sometimes when the boiler is failing to fire, if I turn up the level on the stat, it will kick in, but again, this isn't always the case. So not sure if that helps much!
I'm not actually clear on whether you can buy and fit the thermocouple separate to the whole stat - it certainly doesn't disconnect obviously, like the one for the pilot light on the gas valve does.
I guess if you can't separate them, then it's a moot point which is faulty, but if you can, the thermocouple will only be 1/10 of the price of the stat (which looks to be £50 or so).
So, any advice... does my understanding of what might be wrong make sense, and what options are there for fixing?