OK, so it's a 25+ year old Myson Orion and it started firing up intermittently a while back. It'll fire up and run then randomly there's a clonk and it goes out, only to fire up and start again. An Engineer came out, replaced the gas valve solenoids, decided it was the circuit board and quoted a crazy price to repair, so sent him on his way. Assuming his diagnosis was correct I ordered a refurbished circuit board, fitted it and it's doing exactly the same as it was before!
So, I have tested the room stat, the boiler stat and the fan and programmer and all are OK. The radiator pump is spinning too.
However, I have noticed that the boiler runs fine with the front cover removed, but not when refitted. (Front panel to the boiler, not the panel to the combustion chamber)
Can anyone tell me what this is likely to be? I wondered whether it's the air pressure switch near the fan? Otherwise could it be a leaky seal round the front panel? Gas valve itself?
So, I have tested the room stat, the boiler stat and the fan and programmer and all are OK. The radiator pump is spinning too.
However, I have noticed that the boiler runs fine with the front cover removed, but not when refitted. (Front panel to the boiler, not the panel to the combustion chamber)
Can anyone tell me what this is likely to be? I wondered whether it's the air pressure switch near the fan? Otherwise could it be a leaky seal round the front panel? Gas valve itself?