I have a Potterton Prima F 50 boiler.
I have just changed out the air pressure switch as the boiler wouldnt fire. Turns out the switch for some reason was full of water. Multimeter on the switch showed that it did work, but the fact that it was full of water prevented it from working.
All replaced, turned the boiler on and I am presented with the same fault.
Fan comes to life straight away, but the gas valve and ignition sequence doesn't start up.
Flue is clear of obstructions.
If I draw on the hoses to the APS I can get the boiler to light - so (I think I am fairly safe to assume) that the gas valve and PCB are good.
In one of the APS hoses is a small brass restrictor with a tiny hole through it which appears clear.
Would I be right to lean towards the fan being at fault as it isnt creating the air flow to pull the APS into position?
It was replaced from the original one about a year ago for a non branded replacement. The fan still works and if I put my hand over the flue outside there is quite the flow of air being pushed out.
An intermediary (sp?) flue was fitted last year too and still appears to be in good condition.
Any help would be appreciated before I get an engineer in. I dont know any local friendly ones and I dont want to be taken for a long walk!
Thanks in advance!
I have just changed out the air pressure switch as the boiler wouldnt fire. Turns out the switch for some reason was full of water. Multimeter on the switch showed that it did work, but the fact that it was full of water prevented it from working.
All replaced, turned the boiler on and I am presented with the same fault.
Fan comes to life straight away, but the gas valve and ignition sequence doesn't start up.
Flue is clear of obstructions.
If I draw on the hoses to the APS I can get the boiler to light - so (I think I am fairly safe to assume) that the gas valve and PCB are good.
In one of the APS hoses is a small brass restrictor with a tiny hole through it which appears clear.
Would I be right to lean towards the fan being at fault as it isnt creating the air flow to pull the APS into position?
It was replaced from the original one about a year ago for a non branded replacement. The fan still works and if I put my hand over the flue outside there is quite the flow of air being pushed out.
An intermediary (sp?) flue was fitted last year too and still appears to be in good condition.
Any help would be appreciated before I get an engineer in. I dont know any local friendly ones and I dont want to be taken for a long walk!
Thanks in advance!