boiler over pressurising

Joined
27 Apr 2015
Messages
29
Reaction score
4
Country
United Kingdom
Hi all odd one here.
Firebird enviromax boiler . was gaining pressure up tp 3 bar . to point where safety valve was opening.
Fitted new expansion vessel 12 litre same as original.
Still happening . dropped pressure back to 1bar via safety valve still keeps rising
Thought maybe fill point valve was defective so ive even clamped off flexi hose from fill point outlet.
Any ideas totally mystified .
 
Sponsored Links
Was the communication pipe up to the vessel checked for a blockage?
 
Was the new vessel checked for correct charge? Is it rising without use?
 
Sponsored Links
Hi charged to 1bar before fitting. i wonder if it could be heat exchanger ?
Could be the plate heat exchanger if it has one. Isolate the cold into the boiler and see if it stops rising
 
Ive isolated heat exchanger .it has a valve just before exchanger on water inlet .
Had heating on for 2 hours and its steady at 1.2 bar .I think its heat exchanger !
live and learn .
Thanks for all the replies
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top