Got an odd one here.
My boiler overflow pipe started leaking we estimate sometime around six weeks ago (we noticed it dripping three weeks ago with a bit of green limescale on it, now it's got more limescale).
It only leaks when the hot water comes on for 40 mins in the morning and in the evening, about 20-30 mins after coming on. Obviously no heating at the moment. It drips about once every 20 seconds, and you get a very small puddle on the floor about 10cms diameter on the patio.
However...no loss of pressure. It doesn't leak at any other time and we have no loss of pressure. Our plumber is going to change the valve and the expansion tank just to be sure, but I can't work out why we're not experiencing loss of pressure or, indeed, why the pressure gauge doesn't go shooting up when the boiler is on (as I would have thought a faulty expansion tank would do that).
The system was drained down earlier in the year for three new radiators, would the expansion tank have had to have been repressurised then, as nothing was done to it then?
It's going to cost about £120-130 to have the works done to replace the valve and expansion tank, which isn't terrible but not brilliant either (been expensive year) so just want to rule out anything else that might not cost anything before we have it done.
My boiler overflow pipe started leaking we estimate sometime around six weeks ago (we noticed it dripping three weeks ago with a bit of green limescale on it, now it's got more limescale).
It only leaks when the hot water comes on for 40 mins in the morning and in the evening, about 20-30 mins after coming on. Obviously no heating at the moment. It drips about once every 20 seconds, and you get a very small puddle on the floor about 10cms diameter on the patio.
However...no loss of pressure. It doesn't leak at any other time and we have no loss of pressure. Our plumber is going to change the valve and the expansion tank just to be sure, but I can't work out why we're not experiencing loss of pressure or, indeed, why the pressure gauge doesn't go shooting up when the boiler is on (as I would have thought a faulty expansion tank would do that).
The system was drained down earlier in the year for three new radiators, would the expansion tank have had to have been repressurised then, as nothing was done to it then?
It's going to cost about £120-130 to have the works done to replace the valve and expansion tank, which isn't terrible but not brilliant either (been expensive year) so just want to rule out anything else that might not cost anything before we have it done.