I'm having problems with the CH for my Worcester Bosch Greenstar 42CDi combi boiler. The boiler is basically repeating the same routine:
1) The flame lights, and the temperature display rises rapidly (around 1 degree per second) until it hits around 60 degrees or more.
2) The flame then goes out, and the display drops to below 50 before the flame lights again and repeats the cycle.
The hot water is still fine, but I'm just having this problem with the CH. Yesterday it was showing an E9 error, which means:
According to the manual, these are the suggested check/solutions:
Any ideas of what to look at? Is this a job for a completely inexperienced guy like me, or a professional?
1) The flame lights, and the temperature display rises rapidly (around 1 degree per second) until it hits around 60 degrees or more.
2) The flame then goes out, and the display drops to below 50 before the flame lights again and repeats the cycle.
The hot water is still fine, but I'm just having this problem with the CH. Yesterday it was showing an E9 error, which means:
The display shows alternatively the CH flow temperature and this code. The gradient limitation is active. The primary temperature is rising too fast and the burner has switched off for 2 minutes.
According to the manual, these are the suggested check/solutions:
- Sealed system (pressure between 1 and 2 bar
- Open vented system (enough water in the feed and expansion tank)
- Pump seized or sticking
- Harness disconnected or broken between flue safety stat or overheat stat
- Harness connections from both safety stats to the PCB
- PCB board defective
Any ideas of what to look at? Is this a job for a completely inexperienced guy like me, or a professional?