I’ve had many engineers with no luck, please help!
I am running a glow worm 30 HXI boiler, approx 3 years old. It is a three zone system - one zone is the underfloor heating consisting of 5 loops (approx. 35sqm room), another zone is the rads consisting of 7 rads (6 have TRV's) and the final zone is the hot water cylinder.
The underfloor heating is a suspended floor system under engineered wood and has a polypipe manifold, mixing value and a grundfos alpha 2l pump set on CP1. With these settings, I am achieving flow rates of 1.5l with a flow temperature of 60c (as per the manifold design) and a return temperature of 50c on the UFH manifold.
The main pump is a grundfos UPS 15-50 and is set to speed 2. The boiler flow temperature is set to 63 and the return is typically only 6 degrees lower than flow so around 56. The expansion vessel is set to 1 bar.
My issue is when the underfloor heating is running in isolation I.E. The cylinder and Radiator zones are not calling for heat, after some time in operation the boiler flow eventually reaches 64, then 65.. the return reaches 57, 58 and the overheat protection kicks in and the pilot light is cut. The boiler then remains off for a few minutes and then fires up rapidly before cutting out again within a matter seconds. I have the same issue when the cylinder is the only zone running AND is close to reaching set temperature of 60c.
I have set the range rated the output on the boiler to the minimum of 10kw. I also have a Honeywell bypass value fitted. I’ve tried increasing the main pump to speed 3 and both opening and closing the bypass to see if that helps. Unfortunately, eventually, it still cuts out. I’m not sure where I’m going wrong?
I am running a glow worm 30 HXI boiler, approx 3 years old. It is a three zone system - one zone is the underfloor heating consisting of 5 loops (approx. 35sqm room), another zone is the rads consisting of 7 rads (6 have TRV's) and the final zone is the hot water cylinder.
The underfloor heating is a suspended floor system under engineered wood and has a polypipe manifold, mixing value and a grundfos alpha 2l pump set on CP1. With these settings, I am achieving flow rates of 1.5l with a flow temperature of 60c (as per the manifold design) and a return temperature of 50c on the UFH manifold.
The main pump is a grundfos UPS 15-50 and is set to speed 2. The boiler flow temperature is set to 63 and the return is typically only 6 degrees lower than flow so around 56. The expansion vessel is set to 1 bar.
My issue is when the underfloor heating is running in isolation I.E. The cylinder and Radiator zones are not calling for heat, after some time in operation the boiler flow eventually reaches 64, then 65.. the return reaches 57, 58 and the overheat protection kicks in and the pilot light is cut. The boiler then remains off for a few minutes and then fires up rapidly before cutting out again within a matter seconds. I have the same issue when the cylinder is the only zone running AND is close to reaching set temperature of 60c.
I have set the range rated the output on the boiler to the minimum of 10kw. I also have a Honeywell bypass value fitted. I’ve tried increasing the main pump to speed 3 and both opening and closing the bypass to see if that helps. Unfortunately, eventually, it still cuts out. I’m not sure where I’m going wrong?