I posted this in the plumbing forum without reply thought it was the best place but obviously not can you boy helps I am not overly clued up on boiler controls



My old boiler timeclock with stat is playing up and I want to replace it it has no makers name but says VRT-QT under the cover

It is wired in 3 core and earth as follows

Green/yellow is neutral side of timeclock or terminal 2
Red is terminal 1 or live of timeclock
Yellow is wired to terminal 3
Blue is wired to terminal 4

I want to replace this with a honeywell ST699 programmer and T6360 wall stat but am not sure help

Boiler is a valiant vcw 282 gb

Forgot to say boiler is a combi so no hot water control required just need a stat to regulate temp and a clock to override it when heating is being called for out of timed hours

Many thanks in advance as always
 
Sponsored Links
Perhaps you can post a picture of the timeclock? Somebody might be able to identify it.

I assume you are mistaken in saying that green/yellow is being used as a neutral conductor. It certainly shouldn't be, and if it is, you could be in for a little more work in rectifying that problem before you even get to fitting a new clock.
 
Perhaps you can post a picture of the timeclock? Somebody might be able to identify it.

I assume you are mistaken in saying that green/yellow is being used as a neutral conductor. It certainly shouldn't be, and if it is, you could be in for a little more work in rectifying that problem before you even get to fitting a new clock.

Nope green and yellow are being used as neutral I am going to use 5 core flex to get over this issue :confused:

Can't post a picture as I have just moved house and the camera is all boxed up somewhere sorry :(

I think the clock came originally as part of a boiler pack with the vaillant when it was installed although it does not say Vaillant on it
 
It seems that VRT-QT4 is probably the model number, but it's that old that the Vaillant archive site doesn't have anything other than operating instructions. No wiring diagram, unfortunately.

If it's an S-plan system and you only have four wires, two of which you have already identified, then the other two must be CH and HW demand. With a multimeter and a little playing about with the programmer, I'm sure they can be easily identified. Failing that, trace the wiring back and see which valves it's connected to.
 
Sponsored Links
It seems that VRT-QT4 is probably the model number, but it's that old that the Vaillant archive site doesn't have anything other than operating instructions. No wiring diagram, unfortunately.

If it's an S-plan system and you only have four wires, two of which you have already identified, then the other two must be CH and HW demand. With a multimeter and a little playing about with the programmer, I'm sure they can be easily identified. Failing that, trace the wiring back and see which valves it's connected to.

I afraid you have lost me there with "S" plan. The hot water is instantaneous so the clock which has a built in stat only controls the room temperature and the heating times. It is a rotary clock with pull out segments
 
I have looked for info on your boiler but nothing and I do see neutral on earth wire as a problem so look at something like this because it uses a pair of batteries does not require neutral and it does both time and temperature in one unit. Instead of switching on and off it changes the temperature so no need for frost stat.
And simple two wire connection.
 
It seems that VRT-QT4 is probably the model number, but it's that old that the Vaillant archive site doesn't have anything other than operating instructions. No wiring diagram, unfortunately.

If it's an S-plan system and you only have four wires, two of which you have already identified, then the other two must be CH and HW demand. With a multimeter and a little playing about with the programmer, I'm sure they can be easily identified. Failing that, trace the wiring back and see which valves it's connected to.

I afraid you have lost me there with "S" plan. The hot water is instantaneous so the clock which has a built in stat only controls the room temperature and the heating times. It is a rotary clock with pull out segments

Ah, it's a combi boiler then? Or electrically heated cylinder?

If there is no separate zone valve for the HW, I wouldn't expect it to be necessary to have more than 3 cores + earth at the programmer. Live, neutral, CH demand and Earth is all you should need.

To confirm, are you absolutely sure that green/yellow is being used as Neutral? How so if you don't have a wiring diagram?
 
It seems that VRT-QT4 is probably the model number, but it's that old that the Vaillant archive site doesn't have anything other than operating instructions. No wiring diagram, unfortunately.

If it's an S-plan system and you only have four wires, two of which you have already identified, then the other two must be CH and HW demand. With a multimeter and a little playing about with the programmer, I'm sure they can be easily identified. Failing that, trace the wiring back and see which valves it's connected to.

I afraid you have lost me there with "S" plan. The hot water is instantaneous so the clock which has a built in stat only controls the room temperature and the heating times. It is a rotary clock with pull out segments

Ah, it's a combi boiler then? Or electrically heated cylinder?

If there is no separate zone valve for the HW, I wouldn't expect it to be necessary to have more than 3 cores + earth at the programmer. Live, neutral, CH demand and Earth is all you should need.

To confirm, are you absolutely sure that green/yellow is being used as Neutral? How so if you don't have a wiring diagram?

Yeah sorry about that it is a combi a very old one but a combi all the same.

I am assuming the earth is being used a neutral as it is connected into the neutral terminal on the time clock.

I already have the new clock and stat given to me by an old friend and was hoping to use it so I could fit the stat remotely

Thanks for your help so far
 
why do you want an ST699? They are for Y or S plan systems. Not for combis. They are also daftly expensive for some reason!
 
Best bet would be to trace the wiring back and see how things are connected in the wiring centre, assuming there is one. You're going to have to do this anyway if you end up replacing the cable, so it may as well be done now.
 
why do you want an ST699? They are for Y or S plan systems. Not for combis. They are also daftly expensive for some reason!

Because I was given it brand new in the box but if it is fit for purpose then I have lost nothing :cry:
 
Best bet would be to trace the wiring back and see how things are connected in the wiring centre, assuming there is one. You're going to have to do this anyway if you end up replacing the cable, so it may as well be done now.

Lovely I will take a look tomorrow

Thank you
 
why do you want an ST699? They are for Y or S plan systems. Not for combis. They are also daftly expensive for some reason!

Because I was given it brand new in the box but if it is fit for purpose then I have lost nothing :cry:

You will be able to use it, although the hot water part of the programmer will obviously be redundant. A programmable thermostat would be a far more elegant solution.
 