Local heating engineer came around and suggested replacing BM3 with Boilermate BP (125L capacity). He claimed it to be a straight swap and fully compatible with the existing Potterton Suprima 40 boiler.
Hmmm....is it really a straight swap? Here are at least two things you may want to consider.
Boilermate BP
Boilermate 3
Assuming that the information at the above two sites is correct :
1. The Boilermate III acts as a CH buffer for the heating. This means that the boiler does not heat the radiators directly, but instead heats the water in the thermal store which is then pumped around the radiators. This allows for a smaller boiler to be used. According to the above, the Boilermate BP thermal store water is heated indirectly by the boiler and is not passed around the radiators. The boiler heats the radiators directly. i.e. your boiler may not be large enough to heat all your radiators and may have been sized for the BM III.
2. The Hot Water heat exchange in the Boilermate BP is an internal coil through the thermal store which is the same as my Boilermate II. This arrangement is prone to scaling up. With the Boilermate III, the heat exchanger was moved to an external unit that can be replaced if it scales without having to replace the entire cylinder. Thus the BP design seems to have taken a step backwards.
Just some thoughts - I'm no expert so please do get some professional advice.
Depending on the amount of how water you use, you may find an unvented cylinder to be more efficient. My BM II keeps 125L of water hot all the time and I don't use that much hot water!
The Boilermate BP is a DHW only thermal store. The cylinder can be heated directly by the boiler with the lower boiler coil heating used for the CH circuit to stop sludge entering the cylinder. The boiler works better then.
The internal coil can be descaled. They scale
inside the coil. Full bore valves can be in place to flush the coil through with high pressure mains water and easy fill and trap anti-scale fluids - fill the coil and leave to descale, then flush out.
Many have been replaced by cowboys and all the coil needed was a descale. Anti-scale measures should be in place in any hard water area on any system.
Advance Appliance will supply a stainless store with an external plate heat exchanger - ring them. This guy did one. A search on this forum brings lots up. Ignore the jobbing plumbers who nothing of thermal storage.
//www.diynot.com/forums/viewtopic.php?t=137289&postdays=0&postorder=asc&start=0
Gledhill say:
"This actually makes the new unit much easier
for the uninitiated to understand and has reduced the cost of the Boilermate substantially. Please don't hesitate to call for more info."
The biggest problem with thermal stores is ignorance, as these threads display.