Apologies-I've waded through all the posts on this subject and i think i know the answer to my question but would appreciate confirmation.
Situation- EICR on rental, bonding undersized- whoever renewed the CU in 2010 put the proper size from MET to CU but didn't bother upgrading the rest.
Oddity- the gas meter is under the stairs near the CU, so is cold water stopcock and heating pipes. There's a bit of 6mm from MET to the house side of the meter and onwards to cold water and heating pipes-all fine, easy to replace.
There's another bit of 6mm that drops into the floor void. Supply is TN-S so not an earth rod. DMM had lowest impedance between 6mm and gas pipe so I suspect it runs under the hallway and is clamped to the gas pipe where it enters the house (under the front door somewhere).
My reading of the several posts tells me that since the meter is inside, bonding should be on the customer side of the meter before any branches, visible, mechanically sound, marked. So I don't need to upgrade that 6mm dropping under the floor. True or false?
Ta
Situation- EICR on rental, bonding undersized- whoever renewed the CU in 2010 put the proper size from MET to CU but didn't bother upgrading the rest.
Oddity- the gas meter is under the stairs near the CU, so is cold water stopcock and heating pipes. There's a bit of 6mm from MET to the house side of the meter and onwards to cold water and heating pipes-all fine, easy to replace.
There's another bit of 6mm that drops into the floor void. Supply is TN-S so not an earth rod. DMM had lowest impedance between 6mm and gas pipe so I suspect it runs under the hallway and is clamped to the gas pipe where it enters the house (under the front door somewhere).
My reading of the several posts tells me that since the meter is inside, bonding should be on the customer side of the meter before any branches, visible, mechanically sound, marked. So I don't need to upgrade that 6mm dropping under the floor. True or false?
Ta