Our marvelous combi boiler has 'issues' again, when its cold as usual
Long standing problem was hot water microswitch on changeover valve wasn't always being fully activated when valve activating to get hot water. Changed diaphram and seals but not 100% solved, got worse recently with hot water being very poor and a bad habit of switching off when running hot taps or running bath
Changed microswitch a couple of days ago as that had got wet when I changed the diaphram ages ago, and noticed the changeover valve was now not closing enough to activate the new microswitch, so looked into why water pressure didn't appear to be enough to operate the changeover valve
Pulled out the filter/valve assembly that is at the bottom left of the changeover valve block, and noticed a spring that was jammed sideways and a small plastic plunger that was also rattling around in this block, so I assume thats my problem with water flow as it was somehow jamming/restricting flow. Removed these parts, now no hot water as I assume the valve is permantly shut, hence no water pressure is being diverted to operate the diaphram and moving the changeover valve to operate the switch give us hot water and diverting the water for the DHW system
Just ordered a new filter/valve assembly, won't be here 'till Monday morning so I'm popular with the wife who moans 'at least we had some hot water'
This is the 'only' part I pulled out, the changeover valve operates smoothly by hand as I also changed that 6 months ago and was very badly scaled up and only operating partially and was a pig to remove due to scale build-up, which I assumed was causing the hot water switch issues, until now
What I'm asking is how this simple looking spring/very tiny plastic plunger can cause the changeover valve to now not operate at all and its function as the diagrams I can find don't explain much
And any other suggestion if this doesn't fix it, as I'm at a dead loss as to why the changeover valve is only operating partially
Luckily heating still works, as obviously the changeover valve can't move
Now I've said if we can coax it through to next year its a new boiler time, after 3 circuit board in 3 years and all the other parts. Local parts factors suggested Vaillant ecotec 24/28 as I said I was thinking Vaillant Ecotec 831 as recommended by "which", but at a £800-£1200 for boiler is stretching the budget, not including install and power flush
Reading past comments and the suggested "your lucky to keep it going its an old design now", but wife insists its new and was installed as a new central heating system about 6 years ago now, I suggested it may have been a brand new boiler but how old is that design ......
Long standing problem was hot water microswitch on changeover valve wasn't always being fully activated when valve activating to get hot water. Changed diaphram and seals but not 100% solved, got worse recently with hot water being very poor and a bad habit of switching off when running hot taps or running bath
Changed microswitch a couple of days ago as that had got wet when I changed the diaphram ages ago, and noticed the changeover valve was now not closing enough to activate the new microswitch, so looked into why water pressure didn't appear to be enough to operate the changeover valve
Pulled out the filter/valve assembly that is at the bottom left of the changeover valve block, and noticed a spring that was jammed sideways and a small plastic plunger that was also rattling around in this block, so I assume thats my problem with water flow as it was somehow jamming/restricting flow. Removed these parts, now no hot water as I assume the valve is permantly shut, hence no water pressure is being diverted to operate the diaphram and moving the changeover valve to operate the switch give us hot water and diverting the water for the DHW system
Just ordered a new filter/valve assembly, won't be here 'till Monday morning so I'm popular with the wife who moans 'at least we had some hot water'
This is the 'only' part I pulled out, the changeover valve operates smoothly by hand as I also changed that 6 months ago and was very badly scaled up and only operating partially and was a pig to remove due to scale build-up, which I assumed was causing the hot water switch issues, until now
What I'm asking is how this simple looking spring/very tiny plastic plunger can cause the changeover valve to now not operate at all and its function as the diagrams I can find don't explain much
And any other suggestion if this doesn't fix it, as I'm at a dead loss as to why the changeover valve is only operating partially
Luckily heating still works, as obviously the changeover valve can't move
Now I've said if we can coax it through to next year its a new boiler time, after 3 circuit board in 3 years and all the other parts. Local parts factors suggested Vaillant ecotec 24/28 as I said I was thinking Vaillant Ecotec 831 as recommended by "which", but at a £800-£1200 for boiler is stretching the budget, not including install and power flush
Reading past comments and the suggested "your lucky to keep it going its an old design now", but wife insists its new and was installed as a new central heating system about 6 years ago now, I suggested it may have been a brand new boiler but how old is that design ......