Britony Combi SE - flashing 40 and 80 degrees

Joined
5 Nov 2005
Messages
2
Reaction score
0
Location
London
Country
United Kingdom
I have exactly the same problem as described in this post:

//www.diynot.com/forums/viewtopic.php?p=227531#227531

My Britony Combi SE is not lighting. The 40 and 80 degree lights flash, which indicates lack of system water pressure.

Chris Hutt suggests resolving the problem through using the filling loop to bring pressure up. Only I don't know how to do this... I've searched filling loop with the search facility and I am none the wiser.

Any help gratefully recieved.....

Richard
 
Sponsored Links
I managed to find the filling loop on my boiler and add more water the the system. I can't tell you what a relief it is to have hot water and heating back again. :D

For those of you that are as novice as I - a filling loop is a pipe that releases water into the boiler. Simply release the valve and watch the pressure gauge climb. Although do not over fill.

More can be found here:

http://www.abacusgas.com/air-in-system.htm

Richard
 