nozspark said:A BS EN 60947 is a 2 pole isolator switch not a MCB
I think you're mixing up Zs & Ze.
There are maximum EFL (Zs) values depending on disconnection times & CPD values & types.
For a switch disconnector, you must be thinking of Ze, the incoming supply loop value.
These are:
TN-C-S (PME) = 0.35
TN-S = 0.8
TT = max. 200 (or 100 if NICEIC)
Where did you get this information? Maximum Ze permitted for a TT system is 21ohms. And as the impendance cannot be guaranteed (soil resistivity changing) a 300mA time delayed RCD should be installed at the intake point of TT systems