Found a BS88 35A (20kA breaking capacity) being used on a shower circuit in a house but there aren't any loop impedance readings in the regs to check against. I didn't see any info regarding type on the fuse. Can they be used in domestic C.U.s & if so where do I find the max loop impedances?