We have an open vented S-plan system with an old (but ultimately quite reliable) Ideal Classic NF50 gas boiler. This is one of those older systems where a small controller is in charge of the two zone valves, the pump and the power to the boiler. When one (or both) valves are open and the pump is on, the boiler is powered and makes its own decisions (based on its thermostat) as to when it should burn gas. All radiators have TRVs. There is a bypass valve that should allow water to circulate when all TRVs are closed. [Whether the bypass valve works I don't know.]
On a typical wintery day, with the CH on and the pump running all the time, the normal boiler cycling process sees the boiler burn gas for about 1 minute, then turn the gas off for about 5 minutes, with this cycle repeating continuously.
While that cycling rate is high, it's happily continued doing this (when required) since 1992, so I have no desire to change the above, or upgrade the boiler.
However, just recently, I have noticed lots of fine/small bubble sounds appearing in the pump about 10 seconds after the gas turns off in each cycle. The pump bubble noise lasts about 20 seconds. After they stop, these bubbling sounds don't reappear until the same time in the next cycle. For example, if the boiler is prevented from firing (by turning it off at its isolator) the bubbles never reappear, even though the pump keeps circulating.
Ten seconds is about the time that it would take the pump to get water from the boiler to the pump (and the pump is the first thing that the water from the boiler reaches), so it seems likely to me that the source of the bubbles is somewhere inside the boiler, and that --- for some reason I can't figure out -- the bubbles only enter at the point that the boiler decides to turn gas turns off. Immediately after the pump is the vortex thing below the expansion pipe to the attic -- so the bubbles appear to be being successfully rid from the system either in the pump spindle or the vortex thing, as they don't come back until the next equivalent point in the cycle.
Can any of you suggest a reason why the bubbles would only appear at this point in the cycle?
That's my basic question.
Aside:
I did replace a small towel radiator three days ago, and I'd naturally expect to get (and did get) a small amount of air entering the system as a result. [Not much entered, as there were plenty of isolating valves ... and in any case the radiator was small]. However, I don't think the bubbles I am talking about in my question are related to the radiator change as they only correlate with the turning off of the gas at the boiler, and do not correlate with any other general pump operation. I therefore suspect that the current bubbling thing has been going longer, but I only noticed it after the above radiator fitting as I was paying more attention to the system bedding in. I should add that there are no big bubbles anywhere collecting in any radiators. The sounds represent (at least in my imagination) thousands of small sand-grain-to-lentil-sized bubbles, not the big blobs of air.
On a typical wintery day, with the CH on and the pump running all the time, the normal boiler cycling process sees the boiler burn gas for about 1 minute, then turn the gas off for about 5 minutes, with this cycle repeating continuously.
While that cycling rate is high, it's happily continued doing this (when required) since 1992, so I have no desire to change the above, or upgrade the boiler.
However, just recently, I have noticed lots of fine/small bubble sounds appearing in the pump about 10 seconds after the gas turns off in each cycle. The pump bubble noise lasts about 20 seconds. After they stop, these bubbling sounds don't reappear until the same time in the next cycle. For example, if the boiler is prevented from firing (by turning it off at its isolator) the bubbles never reappear, even though the pump keeps circulating.
Ten seconds is about the time that it would take the pump to get water from the boiler to the pump (and the pump is the first thing that the water from the boiler reaches), so it seems likely to me that the source of the bubbles is somewhere inside the boiler, and that --- for some reason I can't figure out -- the bubbles only enter at the point that the boiler decides to turn gas turns off. Immediately after the pump is the vortex thing below the expansion pipe to the attic -- so the bubbles appear to be being successfully rid from the system either in the pump spindle or the vortex thing, as they don't come back until the next equivalent point in the cycle.
Can any of you suggest a reason why the bubbles would only appear at this point in the cycle?
That's my basic question.
Aside:
I did replace a small towel radiator three days ago, and I'd naturally expect to get (and did get) a small amount of air entering the system as a result. [Not much entered, as there were plenty of isolating valves ... and in any case the radiator was small]. However, I don't think the bubbles I am talking about in my question are related to the radiator change as they only correlate with the turning off of the gas at the boiler, and do not correlate with any other general pump operation. I therefore suspect that the current bubbling thing has been going longer, but I only noticed it after the above radiator fitting as I was paying more attention to the system bedding in. I should add that there are no big bubbles anywhere collecting in any radiators. The sounds represent (at least in my imagination) thousands of small sand-grain-to-lentil-sized bubbles, not the big blobs of air.