Hi
I wonder if anyone has experienced this and may have an answer please!?
In short, when any of the switches disconnects the switched live to the lamps, the lights go off, but a faint buzzing sound can be heard from both lamps – found 30-60Vac between Live and earth – only happened once so far, at night!!!!
What I know:
PME earthling arrangement
The buzzing doesn’t happen all the time, and the first and only time I heard it was last night at around midnight. I am a tall chap and it caught my ear as I walked under the lamp.
Polarity is correct – throughout
Voltage between Switch live and Earth was 60Vac – at time of buzzing
Voltage when it doesn’t buzz is circa 30Vac
Open the circuit breaker with one of the lights switches off – V between SL and N = 1.3Vac
Open the circuit breaker with one of the light switches on – V between SL and N = 0Vac
Two way Intermediate switching works as it should – in all permutations
Insulation resistance is off the scale between P & E and P & N and N & E (installation side)
Measured with digital multi-meter – good one, not tat
Installation:
In my bedroom I have two lights (low energy lamps on pendants – nothing flash) and they are controlled by two number two way switches and one intermediate (MK White plastic single gang switches – the newer ones with smaller switch modules).
One two way is by the door and the remainder are either side of the bed – any switch controls both lights.
The strapping is by way of a 3 core from 2way switch one to Intermediate, and then to the final 2way switch two.
The permanent feed and switch wire are taken from the ceiling rose down to 2way switch one (L1 &L2).
How on earth, when the switches isolate the supply from everything except the lamp and then Neutral, am I getting a potential difference of 60Vac at each ceiling rose between the dead switch live side and earth?
How is it making a circuit when the strapper disconnects the feed to the lighting circuit?
Is it me or is this weird?
Thanks in advance
John
I wonder if anyone has experienced this and may have an answer please!?
In short, when any of the switches disconnects the switched live to the lamps, the lights go off, but a faint buzzing sound can be heard from both lamps – found 30-60Vac between Live and earth – only happened once so far, at night!!!!
What I know:
PME earthling arrangement
The buzzing doesn’t happen all the time, and the first and only time I heard it was last night at around midnight. I am a tall chap and it caught my ear as I walked under the lamp.
Polarity is correct – throughout
Voltage between Switch live and Earth was 60Vac – at time of buzzing
Voltage when it doesn’t buzz is circa 30Vac
Open the circuit breaker with one of the lights switches off – V between SL and N = 1.3Vac
Open the circuit breaker with one of the light switches on – V between SL and N = 0Vac
Two way Intermediate switching works as it should – in all permutations
Insulation resistance is off the scale between P & E and P & N and N & E (installation side)
Measured with digital multi-meter – good one, not tat
Installation:
In my bedroom I have two lights (low energy lamps on pendants – nothing flash) and they are controlled by two number two way switches and one intermediate (MK White plastic single gang switches – the newer ones with smaller switch modules).
One two way is by the door and the remainder are either side of the bed – any switch controls both lights.
The strapping is by way of a 3 core from 2way switch one to Intermediate, and then to the final 2way switch two.
The permanent feed and switch wire are taken from the ceiling rose down to 2way switch one (L1 &L2).
How on earth, when the switches isolate the supply from everything except the lamp and then Neutral, am I getting a potential difference of 60Vac at each ceiling rose between the dead switch live side and earth?
How is it making a circuit when the strapper disconnects the feed to the lighting circuit?
Is it me or is this weird?
Thanks in advance
John