c80ff boiler gone mad!!

Joined
28 Sep 2007
Messages
1
Reaction score
0
Location
Devon
Country
United Kingdom
Hi I have an Ideal c80ff combi boiler which the central heating comes on full blast even when its set for water only,it cannot be regulated and the only way to stop it is shut down completely. Its not like it all the time sometimes it works perfectly normal but when it does go mad its firing up every 2-3 seconds. I had a similar problem 2 years ago and the engineer replaced the PCB, the boiler is about 7 years old surely we don't need a new one!
 
Sponsored Links
No, you dont need a new boiler.

But you do need a competent engineer who can diagnose that the diverter valve gland has leaked water into the DHW flow switch.

Tony
 