Cable diameter for long distance run

RGi

Joined
11 Oct 2018
Messages
11
Reaction score
0
Location
Waterford
Country
Ireland
I'm looking to make an extension lead of over 60m to run a well pump of of the generator after storms or other power cuts. It needs to run the pump which is rated at 2400 Watts. What diameter cable is needed for this to allow for power loss over distance.
 
Sponsored Links
Thanx! It would be great to know how to work it out so I don't have to ask again?
 
Does the pump not need to run in normal (ie not power cut) circumstances? 2.5mm TRS or SWA would do the job (but SWA isn't exactly an extension cable)- might be better getting one of those cheap site gennies from Ebay and not having a 60m cable run
 
Sponsored Links
Does the pump not need to run in normal (ie not power cut) circumstances? 2.5mm TRS or SWA would do the job (but SWA isn't exactly an extension cable)- might be better getting one of those cheap site gennies from Ebay and not having a 60m cable run
Thanx Oldbutnotdead. The pump runs of a buried sheilded mains, but in outages it runs of a genie and 60 m is the closest it can get.
 
I can't get TLC's calculator to give a result

although I can do it manually with a satisfactory resut of 2.5mm² as flameport said.
 
Do you have access to the supply end of the normal power cable for the pump ?
If so, then you could fit a change over switch there and (say) a BS4343 (aka Commando) power inlet. That would avoid the need to run out a long extension lead every time you need it.
 
I can't get TLC's calculator to give a result

although I can do it manually with a satisfactory resut of 2.5mm² as flameport said.
I had a bit of difficulty with it myself. Any chance of the formula or a link to it?
 
Do you have access to the supply end of the normal power cable for the pump ?
If so, then you could fit a change over switch there and (say) a BS4343 (aka Commando) power inlet. That would avoid the need to run out a long extension lead every time you need it.
Good idea but the generator is in a different location unfortunately.
 
What problem(s) were you having?[/QUOTE ]


It is hard to find the answer on the page, the formula would be as easy enough with a calculator. I guess it should be possible to view the page source and get their version of the maths from the HTML or Javascript..?
 