I found the electricians rewiring mothers house about to use twin and earth on a cantenary wire to supply garage from house, I pulled them up on this and what seemed to be a tough black cable was used instead.
This was a twin core and earth with a foil touching the earth screening the cable, at the time I did not question this cable,
was brown, blue with black outer but looks similar to picture.
When the new roof was being fitted to garage the builder was making a hammering sound and with one bang the power went off, tried to reset, but tripped a B32 MCB, a RCD and a 13A fuse, tried to test with multi-meter no fault found, but replacing fuse it ruptured as soon as switched on.
Cable was replaced and all worked, but I felt the builder had done something to cause the problem. New insulation tester arrived, blue shows completely clear, but brown showing around 5 MΩ varying, but cable now disconnected, but still on the catenary wire.
The picture clearly states not suitable for 240 volt. So the big question was the electrical firm responsible for failure or builder? Can't really blame builder if the cable was wrong type and simply failed because of vibration.
I thought it was the cable for the job, but now not so sure, clearly on a canteinary wire cable will flex so neither SWA or T&E are suitable, this cable has around 7 strands in each wire, but not what I would call flex.
I can see no external damage, but since replacing it with flex has cured the problem there is something wrong with it, I have not got step ladders tall enough to cut all cable ties to get it down.
I had expected to find down to earth with insulation tester, but that was not the case. Any ideas as to what cable it is and if rated 240 volt?
This was a twin core and earth with a foil touching the earth screening the cable, at the time I did not question this cable,

When the new roof was being fitted to garage the builder was making a hammering sound and with one bang the power went off, tried to reset, but tripped a B32 MCB, a RCD and a 13A fuse, tried to test with multi-meter no fault found, but replacing fuse it ruptured as soon as switched on.
Cable was replaced and all worked, but I felt the builder had done something to cause the problem. New insulation tester arrived, blue shows completely clear, but brown showing around 5 MΩ varying, but cable now disconnected, but still on the catenary wire.
The picture clearly states not suitable for 240 volt. So the big question was the electrical firm responsible for failure or builder? Can't really blame builder if the cable was wrong type and simply failed because of vibration.
I thought it was the cable for the job, but now not so sure, clearly on a canteinary wire cable will flex so neither SWA or T&E are suitable, this cable has around 7 strands in each wire, but not what I would call flex.
I can see no external damage, but since replacing it with flex has cured the problem there is something wrong with it, I have not got step ladders tall enough to cut all cable ties to get it down.
I had expected to find down to earth with insulation tester, but that was not the case. Any ideas as to what cable it is and if rated 240 volt?