Hi,
SWMBO has deemed that we should stuff the floor joists to our kitchen ceiling with 100mm of *acoustic* insulation (so kitchen chit chat doesn't get overheard in the bedroom above) before we put new plasterboard on.
The joists are ~240mm deep and various lighting and socket cables are clipped to the joists and not in contact with the insulation. In some cases it makes logistical sense (given CH and water pipes) to push the insulation up to be in contact with the floorboards, in other voids it makes more sense to have the insulation at the bottom of the joists. It's either one or the other, so in all cases there is either a ~140mm void above it or below it.
The cables are either clipped above the insulation or below, but in either case will be in the ~140mm void left free by the insulation. At no point are they encased in it and at no point are they in contact with it on one side.
The ceiling voids are enclosed at each end so there is no through flow of air and the rooms above are carpeted including underlay. The ceiling will be standard 12.5mm plasterboard.
Various central heating pipes run in these voids. They never contact the cables and, where they share the same void (between two joists) as cables, have been insulated with 13mm thickness pipe insulation.
Am I right in thinking that this all constitutes REFERENCE METHOD B?
Thus, my 2.5mm radial socket circuits are rated at 21 amps (so, fine on the existing 20 amp RCBO) and my 10mm cooker radial is rated at 57 amps (so, fine on the existing 45 amp RCBO)?
Many thanks
James
SWMBO has deemed that we should stuff the floor joists to our kitchen ceiling with 100mm of *acoustic* insulation (so kitchen chit chat doesn't get overheard in the bedroom above) before we put new plasterboard on.
The joists are ~240mm deep and various lighting and socket cables are clipped to the joists and not in contact with the insulation. In some cases it makes logistical sense (given CH and water pipes) to push the insulation up to be in contact with the floorboards, in other voids it makes more sense to have the insulation at the bottom of the joists. It's either one or the other, so in all cases there is either a ~140mm void above it or below it.
The cables are either clipped above the insulation or below, but in either case will be in the ~140mm void left free by the insulation. At no point are they encased in it and at no point are they in contact with it on one side.
The ceiling voids are enclosed at each end so there is no through flow of air and the rooms above are carpeted including underlay. The ceiling will be standard 12.5mm plasterboard.
Various central heating pipes run in these voids. They never contact the cables and, where they share the same void (between two joists) as cables, have been insulated with 13mm thickness pipe insulation.
Am I right in thinking that this all constitutes REFERENCE METHOD B?
Thus, my 2.5mm radial socket circuits are rated at 21 amps (so, fine on the existing 20 amp RCBO) and my 10mm cooker radial is rated at 57 amps (so, fine on the existing 45 amp RCBO)?
Many thanks