Hi
My oven has a rated maximum load of 3.7kw and the microwave grill has a rated maximum load of 3.6kW. Total maximum load of 7.3kW.
Both are supplied from a single 6 sq.mm cable protected with a 40A MK MCB. The cable length is approximately 12 - 15m long. It has been run clipped to timber joists and is covered with rockwool insulation. The electrician originally had a 32A MK MCB, but increased it to 40A when I requested it.
My hob has a maximum load of 10.8kW ( 5 rings ).
It is supplied with a dedicated single 6 sq.mm cable protected with a 40A MK MCB. The cable length is approximately 15m - 20m long. It has been run clipped to timber joists and is covered with rockwool insulation. The electrician originally had a 32A MK MCB, but increased it to 40A when I requested it.
I understand the principle of diversity and the effect that insulation has on cable ratings.
Do you think that 10 sq.mm cable should have been run or will the 6 sq.mm cables provide sufficient power safely. I think that I may have been wrong to ask for 40A MK MCBs and plan to have the electrician change them back to 32A - the appliances have yet to be wired up.
Any comments ?
My oven has a rated maximum load of 3.7kw and the microwave grill has a rated maximum load of 3.6kW. Total maximum load of 7.3kW.
Both are supplied from a single 6 sq.mm cable protected with a 40A MK MCB. The cable length is approximately 12 - 15m long. It has been run clipped to timber joists and is covered with rockwool insulation. The electrician originally had a 32A MK MCB, but increased it to 40A when I requested it.
My hob has a maximum load of 10.8kW ( 5 rings ).
It is supplied with a dedicated single 6 sq.mm cable protected with a 40A MK MCB. The cable length is approximately 15m - 20m long. It has been run clipped to timber joists and is covered with rockwool insulation. The electrician originally had a 32A MK MCB, but increased it to 40A when I requested it.
I understand the principle of diversity and the effect that insulation has on cable ratings.
Do you think that 10 sq.mm cable should have been run or will the 6 sq.mm cables provide sufficient power safely. I think that I may have been wrong to ask for 40A MK MCBs and plan to have the electrician change them back to 32A - the appliances have yet to be wired up.
Any comments ?