Just in process of changing over the kitchen (part new extension) and have an existing 6mm cable to the hob, but have a new hob which has a rating of 10.7kw. The cable is buried under concrete but is in a conduit, I am thinking the 6mm cable will be a bit on the light side, am I correct. I do not have access to cable rating tables. The new appliances will be connected by an electrician but I will install the cables first.

Any ideas???
 
Sponsored Links
Tables say 38A when enclosed in conduit and 46A clipped direct. Your your current is 46.5.
10mmsq would be the correct size to use in this case.

If its jut the hob the cable is feeding I wouldnt apply diversity either to get down to 6mm sq
 
Many thanks RobFurn, it is just a hob on its own. Will run 10mm now. I was just hoping it would be OK to save the time and £££.
 
After diversity your 6mm² cable on a 32A MCB will be sufficient but will not be able to carry full load (about 45A) which means if you switch on all the hobs the MCB will probably trip. If you want to cater for full load then upgrade to 10mm² cable and a 45A breaker.

Davy

Grr too slow again...
 