I've just had a conversation with an electrician who will be quoting me for a job, which includes installing two 600W towel rail elements.
Each element will be connected to a double pole switched fuse spur as required by the installation instructions.
The instructions also state the circuit must be connected to a 30mA MCB, which isn't an issue for our 4 year old consumer unit.
As there are free slots in our CU he has suggested running a new 2.5mm RADIAL circuit to both towel rails, which will be protected by a 32A MCB. Each of the switched fused spurs will have 13A fuses.
With my limited knowledge, I was surprised at the recommended use of a 32A MCB on this RADIAL circuit. I understand that 32A would be acceptable for a FINAL RING circuit as the load is halved, so shouldn't the new towel rail RADIAL circuit be protected by a 20A MCB, rather than a 32A MCB?
I guess because there are fused spurs, each with 13A fuses, this would actually give the protection required, so does it then really matter about the size of the MCB and it is the speed (30mA) that is important?
I'm sure this is bread and butter to you guys, but I would just like to understand the options a little better.
Each element will be connected to a double pole switched fuse spur as required by the installation instructions.
The instructions also state the circuit must be connected to a 30mA MCB, which isn't an issue for our 4 year old consumer unit.
As there are free slots in our CU he has suggested running a new 2.5mm RADIAL circuit to both towel rails, which will be protected by a 32A MCB. Each of the switched fused spurs will have 13A fuses.
With my limited knowledge, I was surprised at the recommended use of a 32A MCB on this RADIAL circuit. I understand that 32A would be acceptable for a FINAL RING circuit as the load is halved, so shouldn't the new towel rail RADIAL circuit be protected by a 20A MCB, rather than a 32A MCB?
I guess because there are fused spurs, each with 13A fuses, this would actually give the protection required, so does it then really matter about the size of the MCB and it is the speed (30mA) that is important?
I'm sure this is bread and butter to you guys, but I would just like to understand the options a little better.