Hi,

I'd really appreciate some advice on the right type of cable to wire in 6x 35w GU10 spotlights that will be mounted onto a wooden fence. I already have a dedicated garden lighting circuit and will run the connection via a 20A DP switch. Ideally I'd like the thinnest cable possible as I need to feed the cable through some fence battens. Nothing will be at ground level.

Thanks in advance.
 
Sponsored Links
These will have LED bulbs but I'm not a huge fan of LED Strips
 
Sponsored Links
6 x 35 watt at 230 volts = 0.913 amp or 913 mA, so a 1 amp fuse is enough, even when considering volt drop 1 mm² would be ample. Not seen any outdoor rated cable under 1 mm² personally would select a round cable, stuffing glands work better with round cable, and black, as black resists UV light better.

The problem here in Wales is Part P regulations require it to be notified, and that costs £100 plus vat, so I would likely look at extra low voltage, so I do not need to notify, or try to claim it was done before 2004.

Not looked at MR16 compatible lights as to their IP rating, in the old days of tungsten I have fitted MR16 in a well, underwater. But getting a fitting to take GU10 and to seal against the elements may not be easy.
 
6 x 35 watt at 230 volts = 0.913 amp or 913 mA, so a 1 amp fuse is enough, even when considering volt drop 1 mm² would be ample. Not seen any outdoor rated cable under 1 mm² personally would select a round cable, stuffing glands work better with round cable, and black, as black resists UV light better.

The problem here in Wales is Part P regulations require it to be notified, and that costs £100 plus vat, so I would likely look at extra low voltage, so I do not need to notify, or try to claim it was done before 2004.

Not looked at MR16 compatible lights as to their IP rating, in the old days of tungsten I have fitted MR16 in a well, underwater. But getting a fitting to take GU10 and to seal against the elements may not be easy.
Based on this, a .75mm2 cable should also do the job right seeing as it's rated for 6amps which is considerably oversized already?
 
you could use 0.5mm but i would stick with 0.75 as the outer insulation would be thicker and give more protection
 