Hi,

The bottom of my house is a semi basement where we keep the washing machine etc. In the stairwell there's a large 1500 x 600 double panel rad, supplied by 10mm microbore.
When the heatings on it just about gets warm, never hot.

We've also rejigged the area around, the stairwell and added a stud wall to create another small room down there. So what with the radiator not getting hot plus the room it was specced for is now half the size I want to install a smaller rad down there, then install a another rad in the room behind the stud wall.

I also have access to 15mm ch pipework in the adjoining room.

Can I cut and cap off the 10mm microbore at the ceiling? Or can I just join them together? then remove the large rad.

Then T off the existing 15mm (pictured) and run 15mm to the x2 smaller rads from there?
 
Sponsored Links
No don't join together ,or cap. Extend the microbore to one rad. T into the flow and return pipes to supply second rad.
 
Hi, many thanks for the reply:)

The original rad on the 10mm does not get hot, if I tee off that won't it make it even worse?

Reason I wanted to cone off the 15mm as all the rads running off that are piping hot.
 
Sponsored Links
Great cheers:)

What's best to do with the 10mm microbore?
Cap each pipe off as close to the ceiling as possible?

Thanks again
 
As close to the tee's or manifolds where they originate if possible. But close to the ceiling would be a good second best.
 
Is the system pressurised or fed from an f&e tank ? Its not a particularly good idea to have two " dead legs".
The 15 mm pipes currently supply how many radiators ,and what size ?
 
It's going to leave around 6 inches of 10mm dead leg, I know where the tee is as I saw them whilst replacing the floorboards, it would require either ripping out the ceiling or raising floorboards, neither of which is viable now
really.

It's a wb combi boiler, so no tanks etc.
22mm comes off the boiler and runs under the house in a void. The 10mm comes off and supplies x3 rads including the one I want to remove. The rest of the house is on 15mm which is 7 rads.

Thanks again for the replies:)
 
Well 6 inch dead legs are no problem.
So run with your original plan
 