Agile";p="2791167 said:If its a non fanned type projecting about 300mm or less from the wall then I would suggest about 1m from wall to a wood fence.
But that's primarily to allow combustion gasses to disperse better rather than any fear of fire/heat damage. 300 mm from closest part of terminal would probably be enough for that!
The original maker's tech details would probably include a distance to be left unobstructed.
Tony you should probably not give vague guesses!
OP: This is a link to balanced flue clearances:
http://support.ambirad.co.uk/article.aspx?id=10724
The manufacturers instructions over ride these, if you can find them. Your boiler, I assume, is 38,000 BTU/hr OUTPUT, you need to know the MAXIMIM INPUT (regardless of any range rated setting) - which should be on the date badge on the boiler. Then convert to Kw/hr, to use the chart properly.
EDIT: You only need the input to check clearances
This is from the Installation manual on Baxi Partsarena:Hi, its a Baxi WM381RS