I'd appreciate some advice regarding the pressure vessel on my heating system. We have a regular Worcester Bosch 24ri boiler, not a combi and there is an external pressure vessel fitted.
Like most people I bleed all of our radiators once a year at about this time which is what I did the other week. Afterwards I used the filling loop to top up and take up the cold pressure to 1 bar as I always do. This time when I turned everything back on the pressure rose to 2bar but unlike previous year carried on climbing to 3bar then vented outside via the pressure relief valve.
I turned everything off and it fell to zero on the gauge, so then I turned it on again without re-filling. It climbed to just under 2bar ie it's normal running pressure, stopped rising and everything ran normally with all radiators working fine. It has continued to do so for over a week now with no apparent issues.
I researched the high pressure issue and assumed the diaphragm in the vessel had failed. To confirm this I depressed the schrader valve expecting water to appear - no water came out but neither did any air. I had a go at pumping it up at this point, after opening a bleed valve on an upstairs radiator to allow 'room'. The gauge on my pump showed a healthy pressure whilst connected to the vessel but didn't seem to need much pumping to reach this. Then each time as I removed the connector I lost the pressure. Depressing the schrader valve afterwards gave the tiniest 'phut' noise, so clearly nothing was going in.
So my questions...
- Am I OK for now running everything as it stands ie from zero cold pressure rising to just under 2bar when hot or is there likely to a long term issue doing this. I can't get our regular gas engineer out for a couple of weeks at least what with half term etc.
- What could be the problem with the pressure vessel if anything? There certainly doesn't seem to be water in the 'air side' so could it be something as simple as a faulty schrader valve? Any ideas welcome.
Many thanks everyone.
Like most people I bleed all of our radiators once a year at about this time which is what I did the other week. Afterwards I used the filling loop to top up and take up the cold pressure to 1 bar as I always do. This time when I turned everything back on the pressure rose to 2bar but unlike previous year carried on climbing to 3bar then vented outside via the pressure relief valve.
I turned everything off and it fell to zero on the gauge, so then I turned it on again without re-filling. It climbed to just under 2bar ie it's normal running pressure, stopped rising and everything ran normally with all radiators working fine. It has continued to do so for over a week now with no apparent issues.
I researched the high pressure issue and assumed the diaphragm in the vessel had failed. To confirm this I depressed the schrader valve expecting water to appear - no water came out but neither did any air. I had a go at pumping it up at this point, after opening a bleed valve on an upstairs radiator to allow 'room'. The gauge on my pump showed a healthy pressure whilst connected to the vessel but didn't seem to need much pumping to reach this. Then each time as I removed the connector I lost the pressure. Depressing the schrader valve afterwards gave the tiniest 'phut' noise, so clearly nothing was going in.
So my questions...
- Am I OK for now running everything as it stands ie from zero cold pressure rising to just under 2bar when hot or is there likely to a long term issue doing this. I can't get our regular gas engineer out for a couple of weeks at least what with half term etc.
- What could be the problem with the pressure vessel if anything? There certainly doesn't seem to be water in the 'air side' so could it be something as simple as a faulty schrader valve? Any ideas welcome.
Many thanks everyone.