Evening
Just wanted to run something past you and see what suggestions I get back as I am getting to the end of my knowledge but want to check my sanity before spending big bucks getting a local plumber in to sort it out.
1. Baxi Solo 3 PFL50 Boiler went faulty, replaced fan assembly and PCB ( however it has come to light the PCB wasn't actually faulty so now have a spare. Boiler starts working fine for approx two weeks
2. Hot water controlled via a Honeywell 699t controller and honeywell tank stat, room stat is a 6360b, with Honeywell v4073a 3 port valve.
problem I am having is only when the tank stat kicks in does the boiler fire up, not when the central heating is called for.
i've checked the stat is wired up and operating checking for power across terminals 1 and 2 on the thermostat, if it reads 240v then the programmer is fine (which it does ). Check for power across terminals 2 and 3, if it also reads 240v then the thermostat is also fine. You will then need to check the motorised valve.
I have done this and the motorised valve appears to work as when I up the tank stat up to max you can see the lever move all be it very slowly.
However during the water heating cycle the radiators do get hot ...
I am now not sure if to simply swap the valve head or replace the stat
Any ideas greatly appreciated.
Just wanted to run something past you and see what suggestions I get back as I am getting to the end of my knowledge but want to check my sanity before spending big bucks getting a local plumber in to sort it out.
1. Baxi Solo 3 PFL50 Boiler went faulty, replaced fan assembly and PCB ( however it has come to light the PCB wasn't actually faulty so now have a spare. Boiler starts working fine for approx two weeks
2. Hot water controlled via a Honeywell 699t controller and honeywell tank stat, room stat is a 6360b, with Honeywell v4073a 3 port valve.
problem I am having is only when the tank stat kicks in does the boiler fire up, not when the central heating is called for.
i've checked the stat is wired up and operating checking for power across terminals 1 and 2 on the thermostat, if it reads 240v then the programmer is fine (which it does ). Check for power across terminals 2 and 3, if it also reads 240v then the thermostat is also fine. You will then need to check the motorised valve.
I have done this and the motorised valve appears to work as when I up the tank stat up to max you can see the lever move all be it very slowly.
However during the water heating cycle the radiators do get hot ...
I am now not sure if to simply swap the valve head or replace the stat
Any ideas greatly appreciated.