Hi..Is the HW cylinder normally connected to the boiler (via motorised valve/isolating valve/pump/isolating valve) with a non-return valve at the cylinder, ie flow can only enter cylinder at this juncture and not flow back towards boiler? My system is 15yr old, pumped CH, gravity DHW, Baxi back boiler..self-contained ground floor flat. I ask because I dont know if this pipe is blocked at the cylinder inlet (outlet??) or if it is as described above.
Does your motorized valve look like this?
If so you have a fully pumped system; not pumped CH, gravity HW.
The reason so many are confused is that the only reason hot water comes out of the tap is the difference in level between the cold water tank, i.e. gravity. The plumber/heating engineer uses the term "gravity HW" to mean the way the water is circulated from the boiler to the heating coil in the cylinder. In pre-pump days, circulation was due solely to the fact that hot water is less dense than cold, so it rises up the pipe from boiler to cylinder, where the heat is extracted. The density then increases, so the water drops down the return pipe back to the boiler.
There are four connections on a normal indirect HW cylinder:
1. On the very top: this is the Hot water out to the taps etc;
2. At the very bottom (often hidden at the back!): this is the cold water feed from the tank in the loft;
3. About halfway up: this is the feed, via pump and MV, to the coil in the cylinder
4. About 30cm below no 3: this is the return from the cylinder to the boiler
The fact that you have a non return valve suggest that the system has been converted from a gravity HW to a fully pumped. It was put in to prevent reverse circulation.