CH control valves

Joined
9 Jan 2011
Messages
14
Reaction score
0
Location
Herefordshire
Country
United Kingdom
Saunier Duval SB30e boiler
Drayton MA1 3way Valve
Sunvic SZ2301 2way Valve

On my system between the 3 way valve and the HW cylinder there is a 2 way valve. The problem is more times than not there is a hell of a bang from the 3 way valve when HW is called for as if the 2way is fighting the 3way. Is there a problem if I isolate the 2way and just use the 3way to control the CH and the HW.
Both the valves have been replaced.
As for what causes the bang I can only assume there is a wiring problem
Regards
 
Sponsored Links
The usual reason for having both a 2 port and 3 port would be the addition of an unvented cylinder to a Y plan system and as a consequence you must not interfere with the 2 port valve.
 
Mick
Thanks for that. How should the 2 way be wired in? when I took the old one off it had 4 wires, 2 of which were taped up together doing nothing. These I think were from the internal switch
regards
 
Sponsored Links
I should have asked on my other post, do you have an unvented cylinder?
If you do then I advise you to get a G3 certificated engineer to check/repair your fault, the wiring may be manufacturer specific.
 