Hallsy said:
Got a new problem now, tried both the downstairs rad drain cock & one on the boiler but getting no water out?
.
.
.
Do these drain cocks get stuck/blocked?
Yup. Welcome to our world.
When this happens I drain the system through a rad valve, as follows.
Expect there to be some mess, so pick a downstairs room without any carpet - preferably a ceramic tiled floor. It will make life easier for you if the rad is a small one.
Lay a dust sheet and some towels around the rad. Shut both rad valves. Open the vent to confirm that the valves work. If they don't then find a rad where they do.
Get some paint trays and a bucket. Even better, a wet vac. Slowly open the joint between one of the valves and the rad -
NOT the joint of the valve to the pipe. Catch the water that comes out using trays/wetvac/towels/hands etc., until it stops. Uncouple valve from rad. Uncouple other valve from rad (more towels underneath).
Close rad vent. Keeping it level, remove rad from wall with drip trays catching the black yuck that will drip from the holes. Turn the rad upside down to prevent further drips, and put it to one side.
Obtain a suitable connector to couple a hose onto the rad valve. This will usually be either a 3/4" or 1/2" BSP thread, but some rad valves are different - if it is then remove the tail from the rad, gently, connect it back onto the valve, and then join the hose to the rad tail (1/2" BSP).
Now you have control.
Shut off the supply to the F&E cistern, poke the open hose end into the nearest WC, and open the rad valve. Boil kettle and drink tea until system is sufficiently empty.
You might need to drop the hose into the garden to get all of the water out, but you should limit the amount you put on the garden because this is Fluid Category 3 water.
Before refilling the system I would change every DOC washer I could find, so that next time you can drain using one of them.