I have been to a property with a primatic cylinder. Rad upstairs working ok, rads downstairs cold. Have bled them & ensured rad valves are open. 15mm pipework coming down to rads is also cold. Any suggestions on why lower rads are cold ?
 
Sponsored Links
This is a primatic Dave.

If the downstairs rads are each fed from upstairs then they are probably blocked with sludge.

trade questions are best asked in the Combustion Chamber section of this site. Email your registration details and licence number to admin@diynot.

Tony
 
Sponsored Links
Primatic so more than likely pumped heating gravity HW.
ON flow pipe from boiler there is usually an anti gravity valve (brass 3 inches long) these block up and stop correct flow going to rads.
Sharp hit with hammer can free them but support pipe with hand .
Cost about a fiver for new one
 
Pump is working, turned it up to see if that clears the problem, but to no affect. Will try checking anti gravity valve
 
Primatic so more than likely pumped heating gravity HW.
ON flow pipe from boiler there is usually an anti gravity valve (brass 3 inches long) these block up and stop correct flow going to rads.
Sharp hit with hammer can free them but support pipe with hand .
Cost about a fiver for new one
Who stocks them now :?: Not Grahams, Plumb Center or PTS :evil:
 
Plumbcentre def have them saw them other day.
Whether the halfwit on the counter can find them on computer is another story
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top