Hi all,
I have a Vaillant EcoTec 837 that is about 4 years old.
HW operation is fine.
CH operation isn't.
I have the CH temp set to 75º.
When there is a demand for CH, the pump starts, then seconds later the burner ignites and the Flow Temp starts to rise quickly. After approx. 20-30 seconds, the Flow Temp has risen to 75-80º and the burner switches off. The pump enters 'over-run' mode and continues to operate for a further 4-5 minutes. Then the pump stops, and approx. 3-5 seconds later the whole cycle starts again. Pump on, burner on, temp rises rapidly, burner off, pump still running, pump off etc.etc.
I during this time, I noticed that the CH Return pipe was still cold, so couldn't work out why the burner was cutting out. I took a look at d.41 and noticed that it's temperature does not reflect the temp of the Return pipe.
When the burner is ignited, the difference between d.40 and d.41 is around 7-8º, ie. when d.40 gets to the desired temp (75º), d.41 is around 68º, but the pipe is cold.
The result is, that at the moment, the radiators in the house get to be 'warm' after about 3½ hours of the boiler being on. None are even remotely hot.
I have taken a look at someone else's Vaillant boiler (albeit a different model), and their burner stays on the whole time they have a request for heat. I believe that (from reading many forum posts) the burner should 'modulate down' the heat output to match the flow of the CH through the boiler, but I think my problem may be related to the fact the boiler thinks the return temp is higher than it actually is??
Any help or insights would be appreciated.
BTW, I have tried reducing the heat output in d.0 down from 28 to 12, but although it fired for longer, the same effect was happening. I have also tried telling the pump to run at top speed (2), but that had marginal effect as well.
Andy
I have a Vaillant EcoTec 837 that is about 4 years old.
HW operation is fine.
CH operation isn't.
I have the CH temp set to 75º.
When there is a demand for CH, the pump starts, then seconds later the burner ignites and the Flow Temp starts to rise quickly. After approx. 20-30 seconds, the Flow Temp has risen to 75-80º and the burner switches off. The pump enters 'over-run' mode and continues to operate for a further 4-5 minutes. Then the pump stops, and approx. 3-5 seconds later the whole cycle starts again. Pump on, burner on, temp rises rapidly, burner off, pump still running, pump off etc.etc.
I during this time, I noticed that the CH Return pipe was still cold, so couldn't work out why the burner was cutting out. I took a look at d.41 and noticed that it's temperature does not reflect the temp of the Return pipe.
When the burner is ignited, the difference between d.40 and d.41 is around 7-8º, ie. when d.40 gets to the desired temp (75º), d.41 is around 68º, but the pipe is cold.
The result is, that at the moment, the radiators in the house get to be 'warm' after about 3½ hours of the boiler being on. None are even remotely hot.
I have taken a look at someone else's Vaillant boiler (albeit a different model), and their burner stays on the whole time they have a request for heat. I believe that (from reading many forum posts) the burner should 'modulate down' the heat output to match the flow of the CH through the boiler, but I think my problem may be related to the fact the boiler thinks the return temp is higher than it actually is??
Any help or insights would be appreciated.
BTW, I have tried reducing the heat output in d.0 down from 28 to 12, but although it fired for longer, the same effect was happening. I have also tried telling the pump to run at top speed (2), but that had marginal effect as well.
Andy