How I Successfully Changed a TRV
Thanks for the comments above. I thought I'd share that following the above instructions and advice I managed to successfully change the TRV on the Bathroom Towel Rail.
My CH system, is a two circuit with hot water tank, radiators being fed by twin pipes.
I searched more on YouTube and came across this Video from the "The DIY Guy2, which was a bit of a help, and confidence boost (I don't like messing with water pipes!)
How to Change a Thermostatic Radiator Valve Without Draining The System
After watching that I armed myself with the following.
Good Home Polished Chrome-plated Straight TRV from B&Q
Boss White Pipe Jointing Compound from City Plumbing
Two Adjustable Spanners
Radiator Bleed Valve Key
Bucket
Towels
1M Length of Hosepipe
What I Did - Only replaced the actual TRV, keeping the Old Nuts and Olives on the existing Radiator and Pipe
1. Turn off central heating
2. Place plenty of towels around the area to soak up spillages, splashes etc.
3. Put some jointing compound on the treads of the TRV, making sure the decorators cap is on it, and thus closing the valve.
4. Open the bleed valve to release the pressure from the system. I used a length of hosepipe to direct the water from the bleed valve in to the bucket. I kept draining until pretty much all the water had stopped squirting out, there was still a constant dribble, but the video mentioned above and other videos suggested this would always be the case.
5. Close the lock-shield valve. I marked one side of the lock shield valve with a sharpie, and counted the number of turns required to completely turn it off. I counted just shy of 3 full 360degree turns, but made a mental not of the position of the valve. This ensures it is open at the same flow rate as before I started.
6. Empty the bucket from step 3.
7. Loosen the radiator holding brackets. The amount of movement above the existing TRV meant that even undoing the nut, would not be possible without lifting the radiator slightly.
8. Close the TRV. I am not sure this step is necessary, as the next step is against the clock, simply to complete it as quickly as possible.
9. I undid the nut on the radiator side first meaning at worst, only the water from the radiator would need to be accommodated. The water does drain in a glugging motion, but this is managed so long as the TRV is still in situ, while I
10. Undid the central heating pipe side.
11. Jiggle/Lift very carefully the radiator so the TRV can be extracted. Obviously it was important to be very careful here so as not to damage the lock-shield connection. Water will glug out of the radiator, but slowly at this point, and also water will rise up out of the CH pipe, again this isn't an undue amount as there is little to no pressure there. placing a thumb on top of the pipe would easily stem the flow.
12. Place the new TRV in situ, and run down the nuts by fingers (being sure not to cross the threads), and nip up the nuts. I did the CH pipe first so at least the rest of the central heating was sealed once this was done, as the valve was closed with the decorators cap.
13. Once both nuts are nipped up, a thorough drying of the area was done to ensure not a single drop of water was left. That way, if there was any water after the system was re-pressurised, I new it was fresh, and thus a leak.
14. Open the lock shield vale, the appropriate number of turns as in step 5.
15. Using the water fill connection, re-pressurise the system.
16. Check for leaks. Thankfully I have none!
Job Done.
The water in the bucket from changing the TRV was probably about 200-300ml. I'd say this is definitely a job any home DIYer can do. Simply be prepared and methodical. For example, the replacement TRV being ready to go straight in place. There is no point removing the old TRV then starting to mess around with jointing compound on the new TRV.