Changing ST699B programmer to ST6400C

Joined
15 Feb 2007
Messages
3
Reaction score
0
Location
Oxfordshire
Country
United Kingdom
I have tried changing these programmers over using the supplied reference chart enclosed in the box, All the wires matched and connected but on test the ST6400C made a noise like a relay chattering when the heating switch was selected but not when selecting the HW position, The boiler did not fire up when either calling for HW or heating.
Checked all connections in junction box which is a Y plan circuit, Boiler is a Hideaway 40B, I have put the original ST699 back and all OK again the wall stat is an old mechanical one and not sure which Honeywell model it is ....Anyone help please!
 
Sponsored Links
was the st699 wired up for 240v switching (Terminals L-5-8 linked)?
 
the new one doesnt need them as it takes the 240v internally from the LEN connections.
I though i'd ask just in case the ST699 was not wired for 240 this would have meant that you were sending 240 to things that didnt want 240 - get me :confused:

and if you have defo connected the wires correctly on the new one should be HW off, HW on and CH on and LEN. (no CH off)
 