My pump occasionally runs although all 3 actuators (2 zones + Hot water) are closed. Naturally its a bit noisy because its pumping against "blocked" pipes. I have checked the boiler overheat and overrun stats and they are not triggering. Boiler shuts down when actuators closed.
I disconnected all 3 actuator wires to pump+boiler and reconnected them one by one and this showed that one actuator ( 2 port spring return suspect Horstman only a few years old) was supplying volts even though it was closed, but not all the time.
Dismantled it: the cam which operates the microswitch was unworn and the microswitch contacts click normally. Switch mounting is secure.
I am tempted to replace the microswitch (actuator heads are expensive and this valve has been discontinued) but before I do, could this intermittent fault be caused by anything else?