Combi-boiler pressure keeps rising when cold

Joined
30 May 2009
Messages
54
Reaction score
0
Location
Birmingham
Country
United Kingdom
Hi,

I have a Worcester Bosch combi boiler. I'll update the thread with model when I get home. It's like the 24i except it has 2 dials for CH temp and HW temp.

I noticed the pressure gauge was in the red. I went to check one of the rads which usually gets air. No air. I drained one of the rads to get the pressure down to 1.5. Before I went to bed the pressure was back up to 2. This morning it was about 2.5. I haven't been messing with the boiler and I haven't added more water in some months.

Before I call out the plumber is there anything I can check to diagnose the issue?
 
Sponsored Links
filling loop letting by (£10s fix) or hot water heat exchanger leaking (£hundreds)

1 Make sure the filling loop is actually turned off on both taps, and unscrew the flexible hose (turn off the stopcock first if you're worried) Then you'll see if it's letting by.
if not and it still increases, 2. For the dhw exchanger, turn off the cold water supply before the heat exchanger (boiler inlet) and see if it stops increasing. Open a hot tap and see if it drops slowly.
Others may have quicker ideas to check.
 
Is your filling loop letting by? If not then your plate heat exchanger is probably knackered
 
Cheers for those ideas. Will have a go when I get home.

Hope I can disconnect the filling loop, its one those "hard" ones that you need to stick the plastic key in.
 
Sponsored Links
Hope I can disconnect the filling loop, its one those "hard" ones that you need to stick the plastic key in.

Then you can't! Turn off the main stopcock overnight and see if the pressure remains at set level... If it does then boiler needs a new internal filling loop or see if you can make this obsolete and fit an external filling loop.
 
Turn off the main stopcock overnight and see if the pressure remains at set level

If you turn the mains off then it's going to stay at the set level regardless of what's passing, given the boilers mains inlet serves both the loop and the PHE ;)

OP, time to get someone in methinks
 
If you turn the mains off then it's going to stay at the set level regardless of what's passing, given the boilers mains inlet serves both the loop and the PHE ;)
True but If he leaves a tap open overnight, the pressure will drop off it's the dhw exchanger, If it's the loop it will stay the same
 
If this is the cdi 24/28 then it's usually the plates hx pinholed
 
I've been googling, it looks similar to the 27cdi. Can't find the model number on the thing!!

Anyway, I closed the main inlet and opened a hot water tap. The pressure went down. So guessing that's the heat exchanger done in.

I've got a plumber coming tomorrow save me breaking anything.
 
Yep, was the heat exchanger. Decided to get the plumber out instead of trying to fix myself. Turns out I have a Greenstar 30 si which looked way more fiddly than the CDi's I was youtubing.
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top