Comparing output of hydronic plinth heaters

Joined
13 Mar 2019
Messages
873
Reaction score
223
Country
United Kingdom
Looking at heaters from Myson, Smiths and Thermix.
Thermix and Smiths specifications show heat output at flow temperatures from 40-80°C in 5°C steps. Myson specify theirs at two, "∆T 50°C" and "∆T 30°C". For physically similar models, output at ∆T 50 seems to correspond roughly with a flow temperature of 80°C in the others.
What's the difference between these two ways of quoting output?
 
Sponsored Links
I rather doubt there’s much difference between them, after all the physical constraints of these type heaters are pretty much the same across different brands.
 
∆T means the difference between TWO temperatures, so, for example, the temperature inside your house is 25 C & the temperature outside is 5C then the ∆T across the wall is 20C.

Myson are quoting the power emitted when the temperature difference between the hot water flowing in & the water flowing out is 50C and again at 30C. This is really the only correct way to do it - you cant calculate the heat output without knowing the temperature drop across the heater & the flowrate through it
 