Got a small shock from a computer at work today, I was leaning over a PC to plug my usb drive in and my arm touched between two cases, obviously this sparked further interest
Putting my multimeter between the two PC cases revealed 120V, after reading about computer earth leakage recently I decided to pull all of the desking apart to see what was going on, I was quite disturbed by what I found.
The desk is a row of ten pc's inside the cable management at the back I found a four way adapter plugged into a floor box, into the 4 way was another four way, and another, and another
At the other end of the desk, where I received my shock was another floor box with a single four way plugged in.
The floor boxes seem absolutely ancient and on inspection I found that the CPC on the chained set of four ways wasnt making contact because of debris in the socket outlet of the box.
I am now considering myself very lucky that only one PC in the entire row was switched on.
I am a technician, not an electrician. I have informed the schools health and safety officer of the problems and they have asked me to write a report.
What recommendations would you put in the report other than get a trained spark in asap?
I have mentioned the fact that the floor boxes should be replaced and the new ones should have dual earth terminal connections.
I have also reccomended that multi way adapters should not be used and proper sockets provided wherever possible.
I will add that a PIR was carried out by the council last year as well as pat testing.
Got a small shock from a computer at work today, I was leaning over a PC to plug my usb drive in and my arm touched between two cases, obviously this sparked further interest
Putting my multimeter between the two PC cases revealed 120V, after reading about computer earth leakage recently I decided to pull all of the desking apart to see what was going on, I was quite disturbed by what I found.
The desk is a row of ten pc's inside the cable management at the back I found a four way adapter plugged into a floor box, into the 4 way was another four way, and another, and another
At the other end of the desk, where I received my shock was another floor box with a single four way plugged in.
The floor boxes seem absolutely ancient and on inspection I found that the CPC on the chained set of four ways wasnt making contact because of debris in the socket outlet of the box.
I am now considering myself very lucky that only one PC in the entire row was switched on.
I am a technician, not an electrician. I have informed the schools health and safety officer of the problems and they have asked me to write a report.
What recommendations would you put in the report other than get a trained spark in asap?
I have mentioned the fact that the floor boxes should be replaced and the new ones should have dual earth terminal connections.
I have also reccomended that multi way adapters should not be used and proper sockets provided wherever possible.
I will add that a PIR was carried out by the council last year as well as pat testing.