Not Bad Glasshouse, just need to clarify a few things
I take it that the two channels of the programmer are for controlling the UFH and the Central heating
yes
The switched lives from the programmer should power open the motorised valves and the micro switch of these valves be used to send a demand to the boiler via Lr, this will prevent any backfeeds.
The valve connections are normally,
Brown = Valve open
Gray = Permanent live
Orange = switched live
Blue = Neutral
yes ,the connector blocks in the wiring centres are set up like that
You have a neutral connection from both the wiring centre and the programmer going to the UFH, only one is needed.
oh o.k the one from the wiring diagram for the UFH shows L, N and E going to the boiler so I just copied that So i do not need the N back to the boiler?
Not sure why you have that Conn block, the boiler demands should just go to one connection, Lr which will fire the boiler. These switch wires can be bulked up as you say as long as they are switched through the valve. This will enable seperate control of Radiators and UFH.
Yes sorry about that the connector blocks are where all the valves and Programmer and stat is all wired together it was not to show the Lr wires
Does the UFH have any means of temperature control? Yes there are two room stats that all wire through the UFH wiring centre which is basically taking the feed from the programmer in as power and taking the switching cable out the other end which will switch the boiler on if there is demand, the zone valve and UFH pump also are controlled from this wiring centre.,
Is the RF receiver for a remote room stat? yes All that is showing in your drawing is a permanent live and neutral to it. Ideally you want the stat to be powered from the programmer and the switched output from the stat connected to Lr, that way the the programmer will determine on/off periods for the radiators. yes this is the bit that had me stumped , it is (or will be) a Danfoss RETB-RF with a receiver unit RX 1. Is this the right sequence. Channel one of programmer goes to receiver unit (3 c&e) is connected at receiver unit N-N Channel one of programmer to L which is in turn linked to COM the third switching wire then goes to Zone 1 (on) termination of receiver which is terminated to the brown (valve open) of the zone valve back at the wiring centre.I am not sure if this bit is right have asked Danfoss but they are slow to reply.My concern is does the receiver require permanent live?
I would imagine a method of operation as follows:
Permanent live to boiler provides on demand hot water yes
Channel 1 of programmer provides power to room stat and demand from stat opens motorised valve and sends a demand to the boiler via Lr. When the room stat is satisfied or the programmer times out, the valve closes and the demand to the boiler is off.
see above, the orange of the valve will be connected to the Lr
Channel 2 provides power to motorised valve and pump for UFH (via some sort of temp. control) valve opens and switch wire fires boiler via Lr.
As above, when required temperature is reached or programmer times out, the valve closes and the demand is off. yes
If your still unsure about this, tell me how you posted your drawing and i will try to post a similar diagram.